J
Jel
When carrying out a EICR the lighting circuit will show a dead short if you have forgotten to disconnect a lamp somewhere. Is there anyway of getting a true reading without removing all of the lamps?
a compromise would be to test L-N, L-E, N-E with switches off, then short L/N and test to E with switches on.
You could do both live conductors to earth, but of course this would not give a L-N IR. BTW with downlights you would also have to remove the transformers....
it is with those GU10s where you need to pull the fitting out to remove the lamp.
id say you as the inspector would decide this, and if you had coppies of other cetificates and didnt want to disrupt service to building, you could plough on and catch it next time
easy " OK, mr. client, i''ll remove all the lamps and transformers, test, then refix them. that will add £300 to your bill". i know what the answer would be.
as long as you have consulted the person ordering the test first......just covering your arse here.....so no one can say'well he didn't perform the full test'....or something like that.....
The thing that always worries me if it will start tripping when i put new CU. Do you risk it for a biscuit, and waste time looking for a dead short after, or waste time removing lamps and transformers (especially them lovely Auroa bathroom downlights that people love to mastick around and end up brining down half the ceiling when trying to remove one!)
As lamps are a consumable, they should all be removable for changing by a "non-competent" person. You could always offer 2 quotes, one where you remove the lamps and another where the customer takes them all out for you. That way, they can see just how long it takes... :teeth_smile:
Dead short
Jel,
GLENNSPARK,