Hi I’m installing a disabled toilet alarm and they need an extra beacon in the office about 100mt away. Has anyone got any suggestions as to what cable to use for this longer run
 
Hi I’m installing a disabled toilet alarm and they need an extra beacon in the office about 100mt away. Has anyone got any suggestions as to what cable to use for this longer run
maybe? Or maybe not suitable?
 
Now I’m awake, two more thoughts.
1 - is the same way I wouldn’t trust a nest to be a frost stat, for something like this it’s probably not good practise to use wireless.

2 - I’ve fitted a couple that are extra low voltage so volt drop over 100m needs considering

OP is this all within a building or is the office in a different building? Is it a 12/24v dc system?
 
Now I’m awake, two more thoughts.
1 - is the same way I wouldn’t trust a nest to be a frost stat, for something like this it’s probably not good practise to use wireless.

2 - I’ve fitted a couple that are extra low voltage so volt drop over 100m needs considering

OP is this all within a building or is the office in a different building? Is it a 12/24v dc system?

Now I’m awake, two more thoughts.
1 - is the same way I wouldn’t trust a nest to be a frost stat, for something like this it’s probably not good practise to use wireless.

2 - I’ve fitted a couple that are extra low voltage so volt drop over 100m needs considering

OP is this all within a building or is the office in a different building? Is it a 12/24v dc system?
It’s in a factory toilet in the warehouse. Will be 12v DC
 
Is the fire alarm an addressable type? If yes, then way I’ve done it on the past is to fit an input relay onto the fire alarm, connect the toilet alarm to that, then have the fire alarm sounder in the office to activate when the toilet alarm activates. Obviously different tone etc to the normal fire alarm and a bit of fire alarm programming but has worked in some big schools etc
 
Maybe use the cable to switch a relay, and have the beacon powered at the remote (office) end?

And use decent gauge cable to minimise the volt drop.
 
Really need to know the current consumption of the sounder (sorry - beacon!) that's going to be used. The couple of piezo sounders I looked at on the interweb take 250mA to 370mA, so this may not be too much of a problem, unless the sounder is a lot more than that.

1mm sq cable would drop about a volt with those figures.
 
Last edited:
Really need to know the current consumption of the sounder that's going to be used. The couple of piezo sounders I looked at on the interweb take 250mA to 370mA, so this may not be too much of a problem, unless the sounder is a lot more than that.

1mm sq cable would drop about a volt with those figures.

Good point. Could well be not much more than a relay coil.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Sussex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Disabled toilet alarm
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12
Unsolved
--

Advert

Thread statistics

Created
Aaronthesparky,
Last reply from
DPG,
Replies
12
Views
1,981

Advert

Back
Top