Hi I’m installing a disabled toilet alarm and they need an extra beacon in the office about 100mt away. Has anyone got any suggestions as to what cable to use for this longer run
Hi I’m installing a disabled toilet alarm and they need an extra beacon in the office about 100mt away. Has anyone got any suggestions as to what cable to use for this longer run
I must admit I had exactly the same thought before I saw your post.maybe? Or maybe not suitable?![]()
MAINSLINK THE 5KM ORIGINAL SWITCHED LIVE CABLE REPLACEMENT SOLUTION
When time is critical or access is awkward - MAINSLINK the original switched live cable replacement solution, perfect for applications such as lighting and boiler pump overrun!www.rfsolutions.co.uk
Alarm cable will be used for the rest of the system. I just thought with that long a run I might need to size it up a bit. It’s 12v DCThe same cable as you used for the rest of the system.
Now I’m awake, two more thoughts.
1 - is the same way I wouldn’t trust a nest to be a frost stat, for something like this it’s probably not good practise to use wireless.
2 - I’ve fitted a couple that are extra low voltage so volt drop over 100m needs considering
OP is this all within a building or is the office in a different building? Is it a 12/24v dc system?
It’s in a factory toilet in the warehouse. Will be 12v DCNow I’m awake, two more thoughts.
1 - is the same way I wouldn’t trust a nest to be a frost stat, for something like this it’s probably not good practise to use wireless.
2 - I’ve fitted a couple that are extra low voltage so volt drop over 100m needs considering
OP is this all within a building or is the office in a different building? Is it a 12/24v dc system?
I agree, I thought after my post that this is a safety system, and the product I mentioned is not designed for that application, so is a really bad idea!1 - is the same way I wouldn’t trust a nest to be a frost stat, for something like this it’s probably not good practise to use wireless.
Really need to know the current consumption of the sounder that's going to be used. The couple of piezo sounders I looked at on the interweb take 250mA to 370mA, so this may not be too much of a problem, unless the sounder is a lot more than that.
1mm sq cable would drop about a volt with those figures.