Discuss Disabled toilet alarm in the UK Electrical Forum area at ElectriciansForums.net

Maybe use the cable to switch a relay, and have the beacon powered at the remote (office) end?

And use decent gauge cable to minimise the volt drop.
 
Really need to know the current consumption of the sounder (sorry - beacon!) that's going to be used. The couple of piezo sounders I looked at on the interweb take 250mA to 370mA, so this may not be too much of a problem, unless the sounder is a lot more than that.

1mm sq cable would drop about a volt with those figures.
 
Last edited:
Really need to know the current consumption of the sounder that's going to be used. The couple of piezo sounders I looked at on the interweb take 250mA to 370mA, so this may not be too much of a problem, unless the sounder is a lot more than that.

1mm sq cable would drop about a volt with those figures.

Good point. Could well be not much more than a relay coil.
 

Reply to Disabled toilet alarm in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
347
Can someone please guide me on this? I have virtually no experience of home alarm systems. The client has an alarm which had been fitted to her...
Replies
17
Views
1K
Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
625
D
I just had a water leak and had to take the side of the bath off and delighted to also find a few cables going into the floor and shoddily into...
Replies
12
Views
2K
Daughter has bought a house and it has a home security system, G-Tag setup. Issue is the alarm panel displays are pixelated and you cant see...
Replies
1
Views
728

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock