Hi I’m installing a disabled toilet alarm and they need an extra beacon in the office about 100mt away. Has anyone got any suggestions as to what cable to use for this longer run
Discuss Disabled toilet alarm in the UK Electrical Forum area at ElectriciansForums.net
Hi I’m installing a disabled toilet alarm and they need an extra beacon in the office about 100mt away. Has anyone got any suggestions as to what cable to use for this longer run
I must admit I had exactly the same thought before I saw your post.maybe? Or maybe not suitable?MAINSLINK 5KM WIRELESS MAINS TO MAINS 230VAC LINK
MAINSLINK is a plug and play solution to replace a switched live cable. When 230Vac “LIVE” is input to the transmitter; the receiver provides a 230Vac “LIVE” switched output at its screw terminals. When a cable run is awkward or expensive to achieve, the MAINSLINK can be used, saving time and...www.rfsolutions.co.uk
Alarm cable will be used for the rest of the system. I just thought with that long a run I might need to size it up a bit. It’s 12v DCThe same cable as you used for the rest of the system.
Now I’m awake, two more thoughts.
1 - is the same way I wouldn’t trust a nest to be a frost stat, for something like this it’s probably not good practise to use wireless.
2 - I’ve fitted a couple that are extra low voltage so volt drop over 100m needs considering
OP is this all within a building or is the office in a different building? Is it a 12/24v dc system?
It’s in a factory toilet in the warehouse. Will be 12v DCNow I’m awake, two more thoughts.
1 - is the same way I wouldn’t trust a nest to be a frost stat, for something like this it’s probably not good practise to use wireless.
2 - I’ve fitted a couple that are extra low voltage so volt drop over 100m needs considering
OP is this all within a building or is the office in a different building? Is it a 12/24v dc system?
I agree, I thought after my post that this is a safety system, and the product I mentioned is not designed for that application, so is a really bad idea!1 - is the same way I wouldn’t trust a nest to be a frost stat, for something like this it’s probably not good practise to use wireless.