Hello all.

Could any experienced sparkies please please explain to me how RCD tripping times can be adhered to when a PV sytem is integrated into a domestic consumer unit if the inverter takes up to 5 seconds to isolate the AC outputwhich it feed to the domestic supply at the consumer unit. Fed into the buzzbar through the required MCB. Surely safety is compromised. Or am I missing something. I have just completed my first day of a PV course and am a bit confused. after browsing the spec for a SunnyBoy inverter.

Any help appreciated.

Many thanks
 
It should not be sharing an rcd with other circuits.

The proposed V3 of the DTI guide makes it clearer:
"The final connection into a distribution board that contains one or more circuits protected by an RCD, shall be made in such a way that the outgoing circuit for the PV system is not connected into the outgoing side of an RCD installed for the protection of other circuits (ie in a split board – connected into the part not protected by the RCD) ."

Regards
Bruce
 
hi, i'm new to the solar systems myself but don't they cut out straight away if power from supply i.e. mcb/rcd trips? as i thought they had to take a tiny amount of current to operate making a closed circuit. if no supply power to invertor doesn't the circuit become open inside invertor. think that makes some sense?!?!?
 
The G83 spec is cut out within 0.5 second of loss of mains, or 5 seconds if the inverter can withstand energisation with an 180 degree out of phase exitation voltage.

Have a look at some inverter G83 test sheets and you will see the test results.

Regards
Bruce
 
Hi,

I have carried out some tests on this - in my experience disconnection times are still met but increased. However, as the inverter is "allowed" up to 5 seconds to shut down, there is no guarantee that disconnect times will be met under all circumstances (e.g. if the power supplied is close to the instantaneous load). In my opinion this is a big grey area which should have been dealt with clearly before now as safety could be compromised. Best practice is probably to fit a seperate consumer unit or protect with RCBO.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Disconnection time with a PV sytem installed.
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Dave1982,
Last reply from
dougalthedog,
Replies
4
Views
3,131

Advert

Back
Top