I purchased a 95 amp battery isolator and my alternator pushes 95 amps but I'm assuming that it may spike above that occasionally. Should I put a fuse between the two? I am only aware of 100 amp maxi fuses would that save the isolator for damage or do I need to purchase a battery isolator rated for a higher amperage?
 
Alternator output current is self-limiting and will not exceed its spec by much of a margin for long, and hence is very unlikely to damage the battery isolator. A 95A alternator is unlikely even to be able to blow a 100A fuse, which might take hours to react at 130A.

What the fuse might offer is a degree of protection against wiring burnout if the battery or main cables on one side of the isolator become short-circuited, and the battery on the other side dumps a heavy current through it. It's sufficiently unlikely though, that not many installers fit a fuse in that line. Also, the resistance should be kept as low as possible to ensure that the secondary battery receives full charging voltage even when there is load present.
 

Reply to Do I need an inline fuse between my alternator and battery isolator? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

So I'm looking to connect my car's battery directly to a Pure Sine Wave 2000w power inverter So I can use it on job sites etc to power a microwave...
Replies
1
Views
494
Long standing issue on my VW Transporter T4. First noticed under 'lockdown'. Battery drains flat if stood more that 3 - 4 days. Industrial spark's...
Replies
7
Views
408
Hi, My camper has a new 12v battery and I have wired up a split charge relay with a 100 amp blade fuse near van battery and a 100 amp blade fuse...
Replies
7
Views
2K
Long story short im on economy 7 tariff but have 2 types of heaters in my house 1 convector fused socket, 3 storage heaters not fused sockets. So...
Replies
1
Views
756
Hi all, I'm installing a temporary supply to a modular kitchen and need to bring over a new 3PN supply for a new temp consumer unit located...
Replies
3
Views
924

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock