Hi all

Replacing a consumer unit and I always upgrade the tails from the meter to 25mm.

However, the run is an absolute nightmare for a flat im doing a the meter is in the communal hallway.

I'm assuming they have to be upgraded if changing consumer unit?
 
Not if the DNO head is 60a.....or if you consider the load at present to be within the capacity of the existing tails.
 
The onsite guide recomends you do however remember that is just a guide, If the tails are in good condition and are covered by the main service fuse then id leave them in place. IE 100a gets 25mm

I usually allways fit new tails however if as you say its a pig of a job then providing that are large enough and in good nick then they can stay
 
I agree with wirepuller and bigbaddave.

If it's unpracticable to replace the tails then don't do it - providing they're adequate for the load.
 
The onsite guide is purely a "guide" and is mainly aimed at new builds.

Just imagine the size of the OSG guide if it covered all eventualities!!
 
besides most cases would involve the electric company to come and disc/re- connect to the meter - wouldnt it ;)
 
The onsite guide is purely a "guide" and is mainly aimed at new builds.

Just imagine the size of the OSG guide if it covered all eventualities!!

It'd be about the size of the BGB surely that covers absolutely everything :book:
 
The answer is NO, it's like asking do you have to replace the consumer unit if you are replacing the tails, why are you assuming they have to be upgraded? and why do you always replace existing tails with 25mm?
Hi all

Replacing a consumer unit and I always upgrade the tails from the meter to 25mm.

However, the run is an absolute nightmare for a flat im doing a the meter is in the communal hallway.

I'm assuming they have to be upgraded if changing consumer unit?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Do tails HAVE to be upgraded?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
76

Thread Tags

Tags Tags
tails

Advert

Thread statistics

Created
whazza22,
Last reply from
Engineer54,
Replies
76
Views
8,825

Advert

Back
Top