1 x 3A Smoke detector circuit (shows the age as it was a 3A 60898 which I haven't seen before)
It is uncommon to see anything below 6A in domesitc systems, but a few suppliers do ones below 6A but usually C/D curve.
What beggars belief is that someone thought it was a good idea to run those two sub mains from a 40A MCB in the first place! 🤦‍♂️
It probably did not start that way! Sadly it was clearly not a designed process of what and how things would be used :(

Having two sub-mains back to the main DB at least would allow better visibility of total loads if nothing else can be done.
 
Not technically our trade, but telecoms. This was a contractor on behalf of Openreach working on my street this morning.
They had this opened up behind my driveway, with barriers around and warning signs.

In the last half hour, they’ve gone, and left this open.
I just phone Openreach, and they say it will be sorted within 4 hours

F0390C50-85C7-49E9-8C1D-3C95307F73F3.jpeg



4 hours!!!
 
Not technically our trade, but telecoms. This was a contractor on behalf of Openreach working on my street this morning.
They had this opened up behind my driveway, with barriers around and warning signs.

In the last half hour, they’ve gone, and left this open.
I just phone Openreach, and they say it will be sorted within 4 hours

View attachment 94710


4 hours!!!
thats bad to leave the foot way box open, must be rushing around like a lunatic, pair of side cutters handle in the slot drag it back down. lol
 
Nobody's perfect. Easy to forget the obvious sometimes. Or think someone else was doing it.
 
FGS man! Just put it back while muttering about the youth of today and how standards have slipped.

Ya moaning old bugger. :D
Hey... not my job. I might put my back out doing that.

I might put my own barrier around it... but why should I? If someone falls in... its on Openreach

Was thinking of "accidently" falling in myself, just for the compo 😁
 
Hey... not my job. I might put my back out doing that.

I might put my own barrier around it... but why should I? If someone falls in... its on Openreach

Was thinking of "accidently" falling in myself, just for the compo 😁

I'm thinking this isn't very neighbourly.

If some kid or elderly person breaks their leg (or worse) Openreach might pay compensation, but you'll kick yourself for letting this remain open for hours.

If you don't want to move the cover, maybe park your van over it?
 
I'm thinking this isn't very neighbourly.

If some kid or elderly person breaks their leg (or worse) Openreach might pay compensation, but you'll kick yourself for letting this remain open for hours.

If you don't want to move the cover, maybe park your van over it?

Or fill it with concrete. Be very safe then 😀
 
I personally would just drag the cover back on. Five minutes and all safe.
And then you get all the "who touched it last?" problems...

I don't have the proper tools for lifting it... Im not trained to lift it....

I don't even have cones myself that i could put out as a barrier...

I suppose i could put the rabbit run over the top of it..... Without the rabbits 🐰🐰
 
And then you get all the "who touched it last?" problems...

I don't have the proper tools for lifting it... Im not trained to lift it....

I don't even have cones myself that i could put out as a barrier...

I suppose i could put the rabbit run over the top of it..... Without the rabbits 🐰🐰

Dear me. Just do it, nobody will sue you!
 
It’s done.

Random guy in a random van just turned up and dragged it back into place.

I assume it’s one of the workmen that was here earlier, got a phone call and a -------ing to go back and sort it.

That’s my good deed for the day.

All's well that ends well.
 
I don't have the proper tools for lifting it... Im not trained to lift it....
Not an idle concern. I managed to slightly hurt my back when moving one of those lids with the help of another person using basic drain keys (the £8 from toolstation things) and failing to properly keep straight spine while attempting to turn.

Those lids are heavy. Seriously, I think they must be around 50-60kg
 
If some kid or elderly person breaks their leg (or worse) Openreach might pay compensation, but you'll kick yourself for letting this remain open for hours.
I once put my foot down a hydrant hole. It could have been a lot worse but my ankle has not been right since and I assume never will be.
I was walking along, then one step there wss nothing under my foot. Until after a couple feet to gsther momentum I landed on the valve stem and riser connection - slightly off centre so it twisted my ankle and my foot slid off. Nothing broken but it took months for the sprain to heal.
A few inches in any direction and I could have peeled my shin like a carrot.
In my defence, it was hidden in long grass so I couldn't see it - and the airfield manager didn't know it was there. Old wartime airfield, and over the years anything (especially metal to weigh in) that could be nicked had been nicked.
 
I once put my foot down a hydrant hole. It could have been a lot worse but my ankle has not been right since and I assume never will be.
I was walking along, then one step there wss nothing under my foot. Until after a couple feet to gsther momentum I landed on the valve stem and riser connection - slightly off centre so it twisted my ankle and my foot slid off. Nothing broken but it took months for the sprain to heal.
A few inches in any direction and I could have peeled my shin like a carrot.
In my defence, it was hidden in long grass so I couldn't see it - and the airfield manager didn't know it was there. Old wartime airfield, and over the years anything (especially metal to weigh in) that could be nicked had been nicked.

I had a simlar experience at a young age with a missing road side water meter cover, also hidden in long grass. Running fairly quickly when one leg disappeared and that knee tried to bend backwards against the frame. After a couple of weeks the ballon like swelling went away, but I've since had to be careful with that knee - no major issues to date, but occasionally the weakness becomes apparent and I have to be cautious for a week.
 
This is an example of why we get a bad name.

I run an installers group on faceache for EV charge points. Someone has posted these pics in the same make of charger owners group. They said they sent them to an installer who said there happy to add a 7.5kw EVCP onto the installation.

They asked if anyone thought there would be issues on the day as to them it looks a bit untidy.

I’ve seen a couple of so called installers comment saying they could either add the charger to the existing board if there is a spare way. Or connect into one of the Henley’s and run the charger from a third CU! 🤦🏼‍♂️

Now I am far from the worlds best electrician. But I wouldn’t touch that install to add a EVCP without major upgrade. Having been audited on 3 of the installs I’ve done so far I can safely say that they would most likely insist the EVCP was removed or rectification work was carried out on the rest of the installation.

It just irritates me when I see an installation like that and then see so called qualified installers say they would add another board to it as the rest of the installation isn’t their responsibility as they’re only certifying the charger. 😳🤦🏼‍♂️
7D395CFA-E35B-4DB5-BFDA-AFEE433E2A43.jpeg
D8E90570-16BF-45A4-B89E-2F0C89A633C7.jpeg
61C216B0-5C8B-494F-9FA9-C573403CA87C.jpeg
 
Untidy, yes
could do with an upgrade, yes
but what do you see that prevents you from adding a charger on its own small DB?
Max demand for one. It’s apparently a 60A cutout and there’s already 2 CU there And they want to add a 7.5kw charger!

There are a few C2’s there eg with the exposed insulation.

The cabling is a right mess and not supported.

There is no space for another small CU.

I wouldn’t add anything to that installation in its current condition.
 
agree with the exposed insulation, but easy to get DNO out to sort that at no cost to anyone.

messy cabling won’t make a difference to the installation your installing as long as it’s separate.

no space for a CU. Then put it somewhere else, be creative, talk to the customers. There is always a way around a simple issue like this.

max demand. Speak to DNO see if it can be increased. Also what is the current max demand? Two boards does not equal overload. It just means lots of circuits.

the only thing potentiallly holding you back from installing at this installation is max demand.

what I see in that picture is 90% of all the installations I come across. I would have had no work if I said “can’t be done, it’s a mess”.

you install your work to your standard on a separate circuit or a separate consumer unit, no problems.
 
agree with the exposed insulation, but easy to get DNO out to sort that at no cost to anyone.

messy cabling won’t make a difference to the installation your installing as long as it’s separate.

no space for a CU. Then put it somewhere else, be creative, talk to the customers. There is always a way around a simple issue like this.

max demand. Speak to DNO see if it can be increased. Also what is the current max demand? Two boards does not equal overload. It just means lots of circuits.

the only thing potentiallly holding you back from installing at this installation is max demand.

what I see in that picture is 90% of all the installations I come across. I would have had no work if I said “can’t be done, it’s a mess”.

you install your work to your standard on a separate circuit or a separate consumer unit, no problems.
The problem with moving the CU somewhere else is that the CT clamp for the ALM of the charger needs to go around the main tails. So you have to then start either chasing out walls or running trunking to get the CT back to that location If you don’t install the circuit origin near to the main installation.

I didn’t say it can’t be installed on, I just wouldn’t without the cabling supported properly, exposed insulation sorted & cutout fuse upgrade being done.

My point was that some installers were saying they would just stick another CU in and not do anything else.

As I mentioned in the original post. I’ve had 3 of my charger installs audited for OZEV, all without comment or concern raised. I’ve also seen a lot of work that they have pulled up with other installers. So I know the sort of things they look for. If a EV charge point was added to that installation in that condition I can almost guarantee they would say it needs to be removed & remedial work carried out. Which is then done at no cost to the customer, the cost is to be borne by the installer. OZEV will then also withhold the grant payment if not already paid. Or they will rescind it and then it has to be paid back.
 
So I know the sort of things they look for. If a EV charge point was added to that installation in that condition I can almost guarantee they would say it needs to be removed & remedial work carried out. Which is then done at no cost to the customer, the cost is to be borne by the installer. OZEV will then also withhold the grant payment if not already paid. Or they will rescind it and then it has to be paid back.
Not trying to be argumentative, but what gives OZEV the authority to instruct remedial work to be carried out on an existing installation?
 
Not trying to be argumentative, but what gives OZEV the authority to instruct remedial work to be carried out on an existing installation?

They subcontract to a NIC registered contractor. They then inspect the installation for the EV charge point. One of the things they look at is if the existing installation is safe for the charger to be connected.

So if they deem it not to be then the installer has to either remove the charge point and refund the customer or rectify to ensure the installation is safe for connection.

So in this instance they would likely insist the cabling is supported correctly, the exposed insulation is rectified and the cutout is upgraded.

The first could be sorted on the install day and the others by contacting the DNO to sort prior.

I’ve attached what I received when I had my first audit done.

CBF2ED3A-C5DA-4E02-AF13-982D4952E9CB.png

17B1C4EE-636B-4E68-A9DA-02977E0745E6.png
 
Last edited:
So they only instruct after an installation has been completed and upon inspection, if one is carried out, not on the existing installation prior to work starting, which is how I read your post 5278, thanks for clarifying that point.
 
So they only instruct after an installation has been completed and upon inspection, if one is carried out, not on the existing installation prior to work starting, which is how I read your post 5278, thanks for clarifying that point.
Yes they only inspect after by way of audit. Me as the installer is mandated to check prior to installation. If upon audit they deem the existing installation has work that needs to be rectified then yes they do instruct it is done.

I know of 2 people who were told to liaise with the DNO to get a cutout up graded and they also had to upgrade the tails.

They’re not expecting a full EICR. But they are expecting the installation to be in a suitable safe condition for the charger to be added.

Also as an installer you have to be able to say yes to the statement in the ENA form that says
"I confirm that the existing installation is in accordance with the current edition of the Building Regulations Part P (Electrical Safety – Dwellings) and in full compliance with the requirements of the current edition of the UK wiring regulations (BS7671)"

C2 Codes are not in accordance with either part P or 7671.
 
Last edited:
Regarding the above.
Somehow, I'm not seeing much wrong with this. Different, I know, but seems like a version of the old town council 'clerk of works' type system, making sure that things are done well. The main difference being that the upgrades necessary aren't involved in the original job requirements or specification......directly.
It seems like another way of putting the responsibility onto the contractor, as per usual, then providing an inspection system to check all is done correctly.
I used to get situations, whilst pricing for 'off the cuff' council jobs, where I would be expected to notify if there were any other issues with the existing installation and adjust the price accordingly.
I don't know much about it but maybe OZEV is going back to being more thorough about the whole thing....and maybe upsetting some by seemingly being a bit old fashioned.

Note. Then, all council employed electrical contractors had to be NICEIC members..................when it really meant something to be one.
 
Last edited:
Regarding the above.
Somehow, I'm not seeing much wrong with this. Different, I know, but seems like a version of the old town council 'clerk of works' type system, making sure that things are done well. The main difference being that the upgrades necessary aren't involved in the original job requirements or specification......directly.
It seems like another way of putting the responsibility onto the contractor, as per usual, then providing an inspection system to check all is done correctly.
I used to get situations, whilst pricing for 'off the cuff' council jobs, where I would be expected to notify if there were any other issues with the existing installation and adjust the price accordingly.
I don't know much about it but maybe OZEV is going back to being more thorough about the whole thing....and maybe upsetting some by seemingly being a bit old fashioned.

Note. Then, all council employed electrical contractors had to be NICEIC members..................when it really meant something to be approved.
I agree and personally don’t have an issue with my work being checked. I am far from perfect and quite happy to be shown areas I need to improve. I like to think my work is of a good standard. But always willing to learn from the more experienced

I’m actually glad they’re doing it as it was becoming a race to the bottom with EV installs.

Customers naturally want the cheapest option possible for the same equipment. But when you have installers just throwing them onto installations in that condition, often way cheaper than I ever could as they were contracted by a big firm. Then it was affecting the quality of the workmanship and in some cases the safety.

Eg this one. Which was first installed by a so called qualified and competent installer on a 115v commando with the inlet on the supply side. So exposed live pins.

E6525041-A580-48F0-B05A-86A25AE0A085.jpeg


Then when it was ‘rectified it still wasn’t done correctly as it wasn’t using an interlocked socket which is mandatory in a residential setting.

4256E937-2B49-47EE-8837-E5A4FB866D91.jpeg


But the customer saved £200 by using this particular installer.
 
This is another one I found on an EICR that I need to sort.

Tails are ran in SWA to the CU which in a straight line from that position is 4.5m. So will likely be circa 6-8m with the routing. The CU is in the airing cupboard which is in the middle of the upstairs with a bedroom either side and it’s at the back of the house. The meter is on the front left side of the house.

Yet there’s no OCPD for them apart from the DNO fuse. 🤦🏼‍♂️ I do wonder who designs these things at times.

I‘m hoping there’s enough slack in the cable to re-gland and terminate inside a metal clad switched fuse. Can see this being a fun one to do. 🙄

28BF6D59-7313-462A-A36E-3A1E34D6B452.jpeg
 
That will indeed be interesting.
Is the angled piece of board the head is on attached to anything?!
Not many small switched fuses have side entry.
I think I’d be trying to terminate the SWA shorter and crimp onto tails, then use one of those Lewden fuses designed for tails in and out as they aren’t that big. It could replace the isolator too.
 
That will indeed be interesting.
Is the angled piece of board the head is on attached to anything?!
Not many small switched fuses have side entry.
I think I’d be trying to terminate the SWA shorter and crimp onto tails, then use one of those Lewden fuses designed for tails in and out as they aren’t that big. It could replace the isolator too.

I’m going to remove the isolator and put in a metal clad switch fuse. Something like this.


I can hoped drill a hole in the side of that to gland the SWA. Just may have to crimp to extend the SWA inside. But that will be double heatshrink covered if I do. Just need to hope it’s not a slide on cover that the sides come away with. Otherwise I’ll need a rethink.

Although I have a feeling that SWA may only be 16mm

I can’t really crimp it to use a KMF as I need to terminate the SWA into something.

The angled board is fastened the the back board.
 
Seems the fuse box version won’t work.
CE3EB346-4DAD-4C88-8E2C-3F23D5CAC5BC.jpeg


So will have to use this instead.

 
Seems the fuse box version won’t work.
Yes, that is what I meant by most of them not having side entry.
The Chint idea looks possible.
One possible idea/suggestion. Replace the butchered Wiska box, gland the SWA to this, slide behind the angled board and change to tails inside the Wiska box, and then use a KMF?
 
Yes, that is what I meant by most of them not having side entry.
The Chint idea looks possible.
One possible idea/suggestion. Replace the butchered Wiska box, gland the SWA to this, slide behind the angled board and change to tails inside the Wiska box, and then use a KMF?

But isn’t a wiska only rated at max 57a?

So I’d either have to stick a Henley inside or crimp and find a different 100amp rated enclosure?
 
Not electrical. But the award for this years plumber of the year goes to….

89AF1A9C-F3E9-44A9-9756-8092BE6A877D.jpeg


Currently doing an EICR on the same property and the first thing I see (after nearly tripping over the plumbing) as I walk in the garage where the CU is located. But it’s ok as it’s above head height….. 🤔

27C99609-A6C5-459A-8EB3-B843347069FA.jpeg



This is also ok in the bedroom as they know to hold it as they plug/unplug stuff

ECAF73F7-FE2C-420F-980C-53AC6B4470C1.jpeg
 
Seems the fuse box version won’t work. View attachment 94840

So will have to use this instead.


try the wylex one. I always use these. Really robust and side entry possible.

 

Reply to Dodgy trade pictures for your amusement! - 1 Million Views! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock