Great info, thank you all.

Putting in a new earth rod will hardly do any harm so ( even if one is already installed somewhere or other )

In the context of ESB norms, are N + E to be linked or are they separate with E going direct to rod ?

16 Sq OK for earth rod link ? ( std rural 1p supply )

Olddog
 
16mm is more than adequate.
As you have no earthing for the lighting circuits I'd be tempted to install a couple of RCD incomers, one for the main box and one for the "new" box. That way if one tips you'll not lose all your power!
Your only problem will be if you have any existing earth faults!
 
Hi

If you have a TT supply coming in (2 wires) you will need to put a spike into the ground and get the Ze below 200ohms
You have to fit and rcd 100Ma or 30Ma time delay to the main incomer and all socket outlets will require a 30Ma rcd to protect them.

If you have a PME (TN-CS) you can check by doing a Ze test across the incoming supply if you read less than 0.35 its a TN-CS then it would be ok to have the N & E common at the origin of the supply but you still have to run 3 wires to your sub circuits
 
The supply authority DO NOT permit self PMEing.

However, yes, you could test and confirm at the incomer to check the Ze before you contact them so that they can come out and provide a MET, which sometimes is FOC.
 