Shakey
Hi chaps, now dont panic, but I am going to ask a question instead of answering one
went to look at a job this morning
they had ecenomy 7 storage heaters which they have ripped out, i have a few jobs to do, which includes a CU change
current set up is (its on a TT system)
from meter to a 100mA RCD
from there to henley blocks
two sets of tails from henley blocks, one set into fuseboard, and one set into a 'radio teleswitch' which then feeds an isolator and fuse for the storage heaters
Now obviously i will bin the 100ma, 'cause i am putting a twin 30mA board in, but my concern is the radio teleswitch
Now i know basically it 'tells' the main meter to drop to the cheaper tariff, but does it belong to western power distribution?
Can i just rip it out?
My thoughts are that because its after the customers 100mA RCD then it is the customers property. Anyone had any experience of these?