Comes form the NICEIC examples of codes.
I sought guidance as to what to code this if any from an area inspector.
If the db is in an area of sole means of escape but has no signs of thermal damage or loose connections c3.
Now you can argue with this statement all you like but I do see where it comes from.
As bs 7671 calls for non combustible materials to be used or a cu to be installed in a non combustible enclosure, I don't think it's unreasonable to c3 it in an escape route of a dwelling.
Final coding is down to the inspector as the buck will stop with him.
As you know a c3 is still a satisfactory outcome just an improvement of the overall safety and nothing more.
the regulations make no mention of the location of the CU so the code, if any, must be the same regardless of location.
No they don't , however if a fire is to start in a plastic consumer unit and is in the vicinity of the sole means of escape of the dwelling then it's a dangerous situation. Obviously the db should be checked for loose connections during the eicr for possible c1/ c2 codes.
The non combustible regulation came in to contain a possible fire if one was to occur.
Just my take on it Dave.
If fire starts in a consumer unit it is a dangerous situation wherever the CU is located. Especially considering the common habit of people to bury it under all manner of junk, coats etc.
If fire starts in a metal CU which has flammable materials touching it then you can pretty much guarantee that those materials will catch fire.
Not to contain a fire, just to not combust, very different things. CUs are not fire rated to withstand fire for any length of time, thin sheet steel is not suitable for such an application on its own
It will contain it longer than plastic.
That's why it's changed or you might as well leave it as plastic.
To add to the debate. I was under the assumption, that the idea behind A3 non combustible materials, was to remove a potential fuel source from a potential ignition source. Nothing to do with containment.
on the AMD3 fuse boards - we HAVE to remember that its a simply metal enclosure around the dodgy poor quality parts produced by BEAMA...
Although when the reg 421.1.201 came into being, a lot was made of containment. This philosophy, quickly changed when everyone started bumping their gums about intumescent sealing and the fact that a standard A3 CU, has a huge flaw in containment, with a largely flappy poorly sealing lid. :)
So, as I've since heard and read, its about removing the rather doubtful inflammable plastic, with something else, mostly it seems ferrous metal.
Be nice if people could carry out EICRs using gained knowledge and competence as opposed to harping on about the Best Practice Guide and what the NICEIC make up, well we would certainly have less people doing them that is for sure.
But then they would be all old farts like you and me westwood :)
You seem to think that your way is the only way that's called ignorance!
No I think what he is saying, that people conducting EICR's, should have a high level of competency, experience, knowledge etc. Some chaps on here have just left school and are doing them.
Trick is, how do you obtain that 'competency, experience, knowledge etc, in the first place. Kinda chicken & egg thing. :)
Be nice if people weren't so ignorant to think, that reading and listening to people to gain knowledge wasn't a waste of time.
It is an excellent way to gain knowledge working alongside more experienced people whilst referring to relevant Regulations. Who thinks this isn't the case?
Hum... Like kettle calling black ... From the man that doesn't understand the bs 7671 definition of a "circuit"
Lumie,
alanjw,