Hi Gents

Just wanted opinions on the above

I know there are various factors that could sway opinion...

Customers that have a large house with downlights throughout are not too pleased when you give them a four figure quote to rip out the lot......

Cheers

Dave
 
You may just have dropped yourself in it here.....check the actual requirements before scaring clients.
 
You wasn't the kind chap who told one of my customers all the downlighters i had fitted in her bungalow bathroom were 'illegal' and were about to catch fire at any moment and had to be replaced with fire rated ones immediately?

thanks for that!
 
hhaha! fit leds and nothing to worry about about **** going up in flames

It is not the down-lights going up in flames that is the problem. The problem is the 75mm holes, you have cut in a half-hour rated plasterboard ceiling, allowing the fire to spread.
 
Hi Gents

Just wanted opinions on the above

I know there are various factors that could sway opinion...

Customers that have a large house with downlights throughout are not too pleased when you give them a four figure quote to rip out the lot......

Cheers

Dave

If the ceiling is a fire barrier then it will fall under section 527 which requires that the fire barrier not be compromised by the electrical installation.
I would give a C3 code as it is not presenting an electrical danger but is a recommendation of an improvement for safety.
 
Hi Gents

Just wanted opinions on the above

I know there are various factors that could sway opinion...

Customers that have a large house with downlights throughout are not too pleased when you give them a four figure quote to rip out the lot......

Cheers

Dave

If the ceiling is a fire barrier then it will fall under section 527 which requires that the fire barrier not be compromised by the electrical installation.
I would give a C3 code as it is not presenting an electrical danger but is a recommendation of an improvement for safety.

Spot on. Exactly my view too.
 
and do we also seal up the stairwell to stop fire from spreading upstairs? bunk beds in the kitchen.
 
If the ceiling is a fire barrier then it will fall under section 527 which requires that the fire barrier not be compromised by the electrical installation.
I would give a C3 code as it is not presenting an electrical danger but is a recommendation of an improvement for safety.

To a separate property?
 