Hi all
Still got a hangover from saturday but im struggling with one 🤣
EICR, everything tests ok until i press the button on the RCD and it doesnt trip.
Tried 2 spare RCDs same thing.
When i disconnect the sockets Neutral from the busbar it then works.
Type AC 30ma 80A RCD
What am I missing?
Thanks in adavance
Mick
Is the IR N to Cpc definitely OK.
Is it only the socket (i assume ring final) circuit that allows the rcd to trip when disconnected.
It is the most common cause a neutral to earth fault. Have you removed anything plugged into the circuit?
As in #6 are you leaving the cpcs connected when testing.
No i removed and tested after rcd test button wouldnt work
What earthing system is it ?
If it definitely is the ring final, I would be disconnecting/splitting it to see if I could narrow it down.
As soon at the neutrals are disconnected the button works
TNS earthing system
Im going back tomorrow morning see if can solve it
TNS earthing system
Can you temporarily wire in a rcbo to the ring final and see if that fails to trip ?
Redo the IR but leave the cpcs connected. As already mentioned never disconnect cpcs to carry out an IR test.