Dec 16, 2024
Glasgow
Heavily Qualified Electrician / Teacher / Tutor - etc
Hi all
Still got a hangover from saturday but im struggling with one 🤣
EICR, everything tests ok until i press the button on the RCD and it doesnt trip.
Tried 2 spare RCDs same thing.
When i disconnect the sockets Neutral from the busbar it then works.
Type AC 30ma 80A RCD
What am I missing?
Thanks in adavance
Mick
Is there a fault on that circuit?
Is the IR N to Cpc definitely OK.
Is it only the socket (i assume ring final) circuit that allows the rcd to trip when disconnected.
Yeh when i disconnect the neutrals at the DB for the socket ring, the button works
IR is clear on all circuits
Are the CPC's connected to the Protective Earth or disconnected from the terminal during the IR test between Live conductors and Earth?
Reactions: westward10
It is the most common cause a neutral to earth fault. Have you removed anything plugged into the circuit?
Reactions: Tom256
Empty house nothing plugged in,
IR the sockets in question seperate after rcd wont trip. All clear
As in #6 are you leaving the cpcs connected when testing.
No i removed and tested after rcd test button wouldnt work
The IR test is done with the CPC's in the Earth Terminal.
What earthing system is it ?
If it definitely is the ring final, I would be disconnecting/splitting it to see if I could narrow it down.
As soon at the neutrals are disconnected the button works
TNS earthing system
Im going back tomorrow morning see if can solve it
TNS earthing system
Can you temporarily wire in a rcbo to the ring final and see if that fails to trip ?
Redo the IR but leave the cpcs connected. As already mentioned never disconnect cpcs to carry out an IR test.
I done it connected 1st then removed them to test just that circuit
Just a thought but are your spare RCD's Brand New?
https://engx.----------/f/wiring-and-regulations/28594/cause-of-rcd-not-tripping-with-test-switch
The above was posted 3 years ago and they had the same problem turns out all 3 RCDs were faulty
They were second hand parts from a specialised supplier because new parts were not available but you may have the same issue?
Yeh mate they were brand new, i changed the sockets in the lounge and it started working, strange because everything tested out ok before and after changing sockets
Reactions: PS Electrics
Argh....!
We need IR figures, not 'it tests ok'.
Now we're all thinking 'I bet there was a N-E fault. 😅
Reactions: DPG and James
Argh....!
It was >999 on all, tested cables connected and individually, he ce the reason i came on here to ask for ideas
Reactions: HappyHippyDad
Glasgow
EICR - RCD Wont trip on test button
mbu2ns,
mbu2ns,