Before anyone asks I am a qualified spark.. been off the tools for years and getting back into it..
In regards to EICR’s it’s been a while..
Acceptable to add R1 R2 to Ze for ZS or do you all test all 3 anyway? I know it’s not acceptable to ZS and take off ZE to get R1 R2..
 
measure R1+R2 or R2 so you can stick something in the colummn. i usually do R2 with a wander lead to the faceplate screws, (saves taking faceplates off ). then measure Zs where practical (socket adapteror/ rose cover off). educated guesses can fill any blank boxes.tin hat on.
 
I prefer calculating Zs. And if I do I don’t then measure it as well.
If rfc end to end measurements are spot on and the CU is a complete rats nest I might occasionally measure Zs on the rfc at several strategic points, especially spurs if they are identifiable. But only after checking it’s a ring.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Swansea
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Heavily Qualified Electrician / Teacher / Tutor - etc

Thread Information

Title
EICR testing and inspection
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
Eganelectrical,
Last reply from
timhoward,
Replies
2
Views
1,285

Advert

Back
Top