Good morning all,
I have a question about emergency lighting and the requirement of an indicator light stating that it is on mains power and charging.
The centre that I work at has been refurbed and new LED type emergency lights installed at very high level, I don't know what MCB's control them and I noticed that they don't have a L.E.D. indicator showing that they are on mains power.
My question is, do they have to have an indication that they are on mains power and therefore charging? if so where will I find the regulations relating to this?
That's 2 questions,
thank you
Paul
 
BS5266 states that all lights must conform to BS 60589-2-22.

Part of that Standard is that each emergency luminaire must have a green LED indicating charge status.

This would only apply to self-contained emergency fittings however. Clearly a central battery system would not have a charge indicator at every light fitting.
 
As said see if you can see them in the dark. Have you done a test with the key switch to see if they come on? I wonder if the batteries have been connected.
 
I've found a key switch in the wrong position more than once.
 
Hi Strima, sorry for long time to reply. They don’t have key switches. I have to switch the power off on the nearest light circuit with the mcb. I still not seen an LED indicator
Cheers Paul
 
Sometimes the LED indicator can be hard to see even a couple of feet above your head if it is not in the holder properly or has a poor light output
 
Hi Strima, sorry for long time to reply. They don’t have key switches. I have to switch the power off on the nearest light circuit with the mcb. I still not seen an LED indicator
Cheers Paul
So does the emergency lighting come on then when you switched off the mcb?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Camberley
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Maintenance

Thread Information

Title
Emergency Lighting Mains Indication Light
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
Paul Williamson,
Last reply from
Toneyz,
Replies
9
Views
2,927

Advert

Back
Top