So all over Scotland, need to attend each site for xx?? hours/minutes.

Could be fun costing that one!
 
The BS5266 is not just for designing, it is also recommendations for service and testing. and should be tested a minimum of twice per year with a 1 hour discharge, and 1 test being fully 3 hour discharge of all em lighting (iom should still be old 4 times per year) This method is to recycel the nicad batteries by discharging and recharging...any other proceedure for testing such as quick 30 minute tests will actually damage the batteries, by nicad memory effect, where the batteries will never again charge to full capacity.
 
fixed price would be best but there are multiple shops all over .any ideas for a cost .
id assume an hour or two for traveling and three hours on the job for testing ,

any ideas ,do you do anything similar

cheers
come on..
no assumptions here....is there...lol....
 
If it's already been designed and installed and the building use has not changed it's not going I be difficult to test the install is still adequate. Grab a copy of the the relevant BS Though as I once did its quote east reading actually compared to 7671!
 
If it's already been designed and installed and the building use has not changed it's not going I be difficult to test the install is still adequate. Grab a copy of the the relevant BS Though as I once did its quote east reading actually compared to 7671!

As we have all tried to say here, there is nothing wrong with any spark carrying out EM testing, but the key is Period checking and Duration times...but there are still other proceedures to follow, Em log book, Em numbering, onsite period testing, off site contractor testing. So we need BS 5266 to design and service it, BS7671 to install it, and our safety at work act to enforce it....
 
Only government buildings and big companies follow this procedure tho. The rest say need a cert for next week.
 
tazz I have read your threads on fire alarms you are the man!!.Over the decades things have changed soo much,I remember wiring up old analogue 3 wire/ 2 wire systems before smoke detectors were even invented just plain ole call points and sirens.Even EM sounds a bit advanced lol.
 
Only government buildings and big companies follow this procedure tho. The rest say need a cert for next week.

Would recommend you follow the standard for all sites large or small....the log book and cert are proof you carried out all test to the best of your ability, and where stated, any failures you have entered into the log by EM number and location. once you take any contract on, it becomes your responsability to ensure all lighting is fully operational.
 
Understand fully and wouldn't even consider not offering log book. I'm only wee duck in small pond and I do want to know what I'm at, which is why I'm going to jump on me lighting course v soon and that's for my own benifit.
 
It isnt rocket science i promise you....its just a logical test procedure, same as a installation test...your log is the certificate...R1/R2, insulation and earth loop are all tested and then recorded onto the cert, which is technically you log. You number every EM light as you would markup your RBO on a db schedule...........hope this puts it into prespective..
 