I dont think the maths is the same.

When PME and using a supplementary earth rod it takes into account the max current of the installation and this is put into the equation which brings up a low Ra value.[/QUOTE]
 
When put into maths it requires a stupid low Ra value which cannot in reality be sustained.

That's my understanding?
Yes we did some calcs at college when we did the course. It was nigh on impossible. I think 3 earth rods 1 meter apart 2.4 meters deep might do it. Depending on resistivity of the earth.
So they have given us a solution to the problem that is pretty pointless.
 
I dont think the maths is the same.

When PME and using a supplementary earth rod it takes into account the max current of the installation and this is put into the equation which brings up a low Ra value.
[/QUOTE]
You don’t take the pme into account when doing the maths as the rods are there in case you loose the neutral, thus loose the pme.
 
The major point of TT for ev is in case of dropped neutral on supplier side.

That in itself is pretty rubbish that we have to prepare for faults that are nothing to do with our regs and are in the control of the DNO’s.

So we need to know that the earth rods being put in at the origin are adequate without the pme if the neutral is lost by DNO
 
These are not my suggestions, they are what I was taught on the City & Guilds course in EV charging that I did. I dare say that anyone else who has completed the course would have been taught the same.

If these 'suggestions' amuse you, why not e-mail Bill Allan of NAPIT and laugh loudly at him while you tell him that you know more about EV charging than he does. Meanwhile, kindly desist from trying to me appear foolish. Fair enough?

https://professional-electrician.com/18th-edition/changes-introduce-shock-risk

I don't claim to know more about EV charging than anyone. However is is obvious (hopefully) that introducing an extraneous earth potential into an installation then connecting it to a big piece of exposed metal (car) goes against the basic principles of protection against electric shock.

I am not trying to make you appear foolish, I have no need to do this. By suggesting that one can laugh loudly in an email you have achieved this appearance without my input.
 
if the prohibition of PME for EV chargers is to eliminate risk if the supply N is lost (as with metalclad caravans) the I can't see any reason to differentiate between inside or outside. a fault occuring would have a similar result, in or out. then, i have not done any research on EV so my knowledge is limited.

If the vehicle is inside then it is, technically, within the equipotential zone and becomes no different to any other exposed, earthed, metal in the building. The car being charged in the garage presents the same hazard as the class 1 freezer in the garage.
 
The attached scan is from section 5.3.3.3.1, page 32 of the Code of Practice for Electric Vehicle Charging Equipment Installation. The section heading is: Providing a TT earthing system for the charging equipment.

So how do you ensure that the zone of influence of the earth electrode does not overlap the zone of influence of any metalwork connected to the PME earth?
Do you trace and map out every gas and water pipe, buried structural steel etc?
Do you get accurate maps from the DNO showing the extent of the zone of influence of every buried PME electrode in the street, street furniture, repurposed PILC cable etc?
 
So how do you ensure that the zone of influence of the earth electrode does not overlap the zone of influence of any metalwork connected to the PME earth?
Do you trace and map out every gas and water pipe, buried structural steel etc?
Do you get accurate maps from the DNO showing the extent of the zone of influence of every buried PME electrode in the street, street furniture, repurposed PILC cable etc?

The link I posted from WPD, gives their views on such (for those who've not read it);
The earthing considerations for the connection of electric vehicle charge points are firstly the type of earthing arrangement (PME, SNE or TT) and secondly the required segregation between these different earthing types. The requirements of the Code of Practice for the installation of EV charging equipment makes the use of protective multiple earthing (PME) prohibitive and steers installations towards a TT setup. However the IET Wiring Regulations (Guidance note 7) requires segregation of a minimum of 10m between the PME and TT earthing systems. We understand that this requirement will restrict installations in the street and therefore we have recalculated the requirement using modelling specifically for a street side application. As a result we can reduce the distance so that a balanced three phase demand utilising a TT earthing system will require segregation from the WPD earthing system by a minimum of 0.3m and a single phase or unbalanced connection would require a segregation of 3.6m.’
 
Yes we did some calcs at college when we did the course. It was nigh on impossible. I think 3 earth rods 1 meter apart 2.4 meters deep might do it. Depending on resistivity of the earth.
So they have given us a solution to the problem that is pretty pointless.

What formulae were used?

Seem crazy now, that the 18th draft was considering going earth rod mungus or is that something different?
 
How many electricians install an earth rod for an outdoor socket on a pme system, supplementary or otherwise. Cant see much difference myself.
 
just for instance, a trailing lead across a pavement for a booster charger, admittedly not as big a target, but there are many class I appliances that could be plugged in to such.
Surely similar considerations should be given to outdoor sockets, especially as there is no end to what some mugs will plug into them.
 
Hi,

I got back in touch with the installer.....and sent the following email:

"There is something I was looking to clarify with you in relation to my recent charger installation.

As you know the charging unit is located internally in my garage, as my primary intensions will be to charge whilst the car is parked inside the garage overnight.

However, as the selected location of the charging unit is next to the garage door, I had also anticipated that the unit could be used for outside charging as the cabling could easily run under the garage door.

A friend of ours has a similar EO installation where their charger is also located internally next to the garage door like ours, therefore enabling him to charge either indoors or outdoors.

However, he had pointed out to me that in order to charge outside there are some safety regulations required on the earthing requirements of the install; such that their installer had advised that an Earthing rod would be required.

It appears within my installation, the charging unit is setup to use our domestic earthing system (i.e. T-N-CS (PME)) and not via an Earthing rod?

I had checked out the EO website regarding this requirement, and as per the latest 18th edition regulations (Section 722.411.4.1) it does appear to state that PME earthing systems should not be used for any outdoor charging, and that the primary mechanism should be an Earthing rod for the EO charging unit.

It looks like this regulation is primarily there as a protection against the risk of fatal shock hazards caused from faults within the supply network of earthing systems (i.e T-N-CS (PME))

So having come across the above information, I am naturally concerned particularly on the safety aspects if one was to charge outside?

As I’ve mentioned, the primary use will be charging indoors, but with the possibility of future and occasion-use for outdoor charging in mind – Hence the selected location of the charging unit is located next to the garage door; allowing cabling to reach the front of the driveway.

Prior and during the install, I was not made aware that there would be any issues based on my anticipated use-cases; and likewise there were no earthing requirements highlighted for consideration.

However, these latest regulations seem to suggest otherwise, and therefore I would want to obtain clarification that I am safe to use the charger as intended (i.e. both indoors and outdoors)

Or is it the case that the earthing setup will need to be changed to cater for outdoor use i.e. Earthing rod?

If an Earthing rod must be used, would I still be able to charge safely whilst parked inside the garage as per my primary intended use i.e. assessment of any extraneous conductive parts that are simultaneously touchable with the vehicle or charge point etc."
 
Hi,

I got back in touch with the installer.....and sent the following email:

"There is something I was looking to clarify with you in relation to my recent charger installation.

As you know the charging unit is located internally in my garage, as my primary intensions will be to charge whilst the car is parked inside the garage overnight.

However, as the selected location of the charging unit is next to the garage door, I had also anticipated that the unit could be used for outside charging as the cabling could easily run under the garage door.

A friend of ours has a similar EO installation where their charger is also located internally next to the garage door like ours, therefore enabling him to charge either indoors or outdoors.

However, he had pointed out to me that in order to charge outside there are some safety regulations required on the earthing requirements of the install; such that their installer had advised that an Earthing rod would be required.

It appears within my installation, the charging unit is setup to use our domestic earthing system (i.e. T-N-CS (PME)) and not via an Earthing rod?

I had checked out the EO website regarding this requirement, and as per the latest 18th edition regulations (Section 722.411.4.1) it does appear to state that PME earthing systems should not be used for any outdoor charging, and that the primary mechanism should be an Earthing rod for the EO charging unit.

It looks like this regulation is primarily there as a protection against the risk of fatal shock hazards caused from faults within the supply network of earthing systems (i.e T-N-CS (PME))

So having come across the above information, I am naturally concerned particularly on the safety aspects if one was to charge outside?

As I’ve mentioned, the primary use will be charging indoors, but with the possibility of future and occasion-use for outdoor charging in mind – Hence the selected location of the charging unit is located next to the garage door; allowing cabling to reach the front of the driveway.

Prior and during the install, I was not made aware that there would be any issues based on my anticipated use-cases; and likewise there were no earthing requirements highlighted for consideration.

However, these latest regulations seem to suggest otherwise, and therefore I would want to obtain clarification that I am safe to use the charger as intended (i.e. both indoors and outdoors)

Or is it the case that the earthing setup will need to be changed to cater for outdoor use i.e. Earthing rod?

If an Earthing rod must be used, would I still be able to charge safely whilst parked inside the garage as per my primary intended use i.e. assessment of any extraneous conductive parts that are simultaneously touchable with the vehicle or charge point etc."
Ha ha, your electrician will be thinking "sxxx, he knows his stuff!" :D
I think that's well worded hyeung, however from the little I've seen of your posts you're not one to just accept a half answered question. I wonder what you will do if he just says says 'yes, it's fine for outside'! :)
Let us the know the response and then we can start the discussion all over again.
 
Hi,

I got back in touch with the installer.....and sent the following email:

"There is something I was looking to clarify with you in relation to my recent charger installation.

As you know the charging unit is located internally in my garage, as my primary intensions will be to charge whilst the car is parked inside the garage overnight.

However, as the selected location of the charging unit is next to the garage door, I had also anticipated that the unit could be used for outside charging as the cabling could easily run under the garage door.

A friend of ours has a similar EO installation where their charger is also located internally next to the garage door like ours, therefore enabling him to charge either indoors or outdoors.

However, he had pointed out to me that in order to charge outside there are some safety regulations required on the earthing requirements of the install; such that their installer had advised that an Earthing rod would be required.

It appears within my installation, the charging unit is setup to use our domestic earthing system (i.e. T-N-CS (PME)) and not via an Earthing rod?

I had checked out the EO website regarding this requirement, and as per the latest 18th edition regulations (Section 722.411.4.1) it does appear to state that PME earthing systems should not be used for any outdoor charging, and that the primary mechanism should be an Earthing rod for the EO charging unit.

It looks like this regulation is primarily there as a protection against the risk of fatal shock hazards caused from faults within the supply network of earthing systems (i.e T-N-CS (PME))

So having come across the above information, I am naturally concerned particularly on the safety aspects if one was to charge outside?

As I’ve mentioned, the primary use will be charging indoors, but with the possibility of future and occasion-use for outdoor charging in mind – Hence the selected location of the charging unit is located next to the garage door; allowing cabling to reach the front of the driveway.

Prior and during the install, I was not made aware that there would be any issues based on my anticipated use-cases; and likewise there were no earthing requirements highlighted for consideration.

However, these latest regulations seem to suggest otherwise, and therefore I would want to obtain clarification that I am safe to use the charger as intended (i.e. both indoors and outdoors)

Or is it the case that the earthing setup will need to be changed to cater for outdoor use i.e. Earthing rod?

If an Earthing rod must be used, would I still be able to charge safely whilst parked inside the garage as per my primary intended use i.e. assessment of any extraneous conductive parts that are simultaneously touchable with the vehicle or charge point etc."

In response I got the following....

"Your understanding of the earthing requirements is correct, if you wish to use your charger to charge the car outside then regulations state the use of a TT earth is required, if the charge point is to be used inside then connection to your house earth is recommended.

Looking back at the information you provided, you requested that the charge point be installed inside the garage and we have assumed that this would be for the purpose of charging inside, we will look to clarify this to all customers going forward.

If the charge point is fitted outside and connected to a TT earth then it should not be used inside the garage as this is a different earthing zone(house earth)

Hope this clarifies matters.
Regards"

It seems from his response it suggest that I cannot have it both ways?

So when the charger is inside, its recommended that I use house earth and can only charge whilst inside.

If I want to charge outside, then the charger unit should ideally sit outside and an earth rod used (TT); and in this case I cannot use this for charging inside.

There is no both?
However, a friend of ours has the exact same EO installation (but his is tethered). It has been installed in his garage, and he uses this inside but has been installed with an earth rod for outside charging?
See attached photos.
The car forums that I've been on, have also shown similar folk using their charge in their garage for outside charging.

I've gone back to clarify with the installer that I can definitely not do it both ways?
Perhaps I should contact the manufacture of the unit and get their side of the story as well? If they say the same, then i'm happy to walk away and stick to the setup that I have - which is what i'd primarily use it for. It's just that I've seen others use it both ways, which either means it possible and fine, or perhaps in reality is genuinely isn't a safe approach?

What are your thoughts??
 

Attachments

  • 67802807_10157523160208466_5041270399719964672_n.jpg
    67802807_10157523160208466_5041270399719964672_n.jpg
    97 KB · Views: 22
  • 67836457_10157523159468466_2661591697187667968_n.jpg
    67836457_10157523159468466_2661591697187667968_n.jpg
    114.2 KB · Views: 22
Ha ha, your electrician will be thinking "sxxx, he knows his stuff!" :D
I think that's well worded hyeung, however from the little I've seen of your posts you're not one to just accept a half answered question. I wonder what you will do if he just says says 'yes, it's fine for outside'! :)
Let us the know the response and then we can start the discussion all over again.

I think more thanks to my sparky buddies on this forum...sounds like I know my stuff :)
 
This is a case of technology moving on at a far greater rate than the relevant regulations that should oversee it.

I personally see very little difference to the following,

someone touching a car (on charge) and at the same time, ornate iron gate with good foundations

someone touching a car (on charge) and at the same time, a water pipe inside the garage

someone sat leaning against a well grounded metal fence whilst tinkering with there electric lawnmower

I would like too see all items used outside the house being fed from an ungrounded isolating transformer with rcd protection.
best of both worlds?
 
This is a case of technology moving on at a far greater rate than the relevant regulations that should oversee it.

I personally see very little difference to the following,

someone touching a car and ornate iron gate with good foundations

someone touching a car and a water pipe inside the garage

someone sat leaning against a well grounded metal fence whilst tinkering with there electric lawnmower

I would like too see all items used outside the house being fed from an ungrounded isolating transformer with rcd protection.
best of both worlds?
Other than the fact the car has four big rubber well insulated wheels.
 
I applaud your approach here hyeung, but more so the fact that from your first pic it seems you have an impossibly tidy garage...please tell me that you simply shifted a load of sh*t out of the way before taking the photo...

Hahah the garage is "sorta" tidy, but only becos I've managed to stack things up on one side of the garage. The other side I use to park the car. In that photo I had to move all the sh*t to the other side.....so they could install the cabling/trunking and the charge unit.

I don't think i'm getting anywhere with this.
I don't understand why others are able to have their unit in the garage and charge inside and out...with the earth rod setup. Am I missing something? Is my installer just trying to put me off and keep what I've got.
I've emailed the Manufacturer to also confirm use-cases for both inside and outside charging.

Wish I knew all this before the install, as i'd ended up not getting the EO unit; and probably got something that didn't have any earth rod requirements i.e. Zappi or more pricy Andersen.
 
Hahah the garage is "sorta" tidy, but only becos I've managed to stack things up on one side of the garage. The other side I use to park the car. In that photo I had to move all the sh*t to the other side.....so they could install the cabling/trunking and the charge unit.

I don't think i'm getting anywhere with this.
I don't understand why others are able to have their unit in the garage and charge inside and out...with the earth rod setup. Am I missing something? Is my installer just trying to put me off and keep what I've got.
I've emailed the Manufacturer to also confirm use-cases for both inside and outside charging.

Wish I knew all this before the install, as i'd ended up not getting the EO unit; and probably got something that didn't have any earth rod requirements i.e. Zappi or more pricy Andersen.

I will never suggest someone goes against what the regulations state, especially a customer. However, I will refer you to my post #63. The facts from the report show that absolute worse case scenario (so in reality nowhere near this) you have a 1 in a million additional chance of risk of death or serious injury from using a car charger with PME earthing.
As a professional I have to say don’t use it outside, but if you decide to you have the risk explained above.
 
I will never suggest someone goes against what the regulations state, especially a customer. However, I will refer you to my post #63. The facts from the report show that absolute worse case scenario (so in reality nowhere near this) you have a 1 in a million additional chance of risk of death or serious injury from using a car charger with PME earthing.
As a professional I have to say don’t use it outside, but if you decide to you have the risk explained above.

Yeah I downloaded that pdf...intresting indeed.
Can I ask, if you had TT earthing which makes it fine for outside. Can you not use this inside? What is the issue with that?

The odds/risk are so low, but never the less I wouldn't personally risk it - PME outside charge? Would you? Its more the thought that you are putting others at risk. With young kids in the family enough said...
 
Regulation 722.411.4.1 unequivocally and unambiguously states that: "a PME earthing facility shall not be used as the means of earthing for the protective conductor contact of a charging point located outdoors OR that might reasonably be expected to be used to charge a vehicle located outdoors ..... ". Ergo it is self-evident that the EV charger which has been installed adjacent to the entrance of the OP's garage could be reasonably expected to be used to charge a vehicle located outdoors. All the OP need do to create this very scenario would be to park his/her car outwith the garage then connect the charging lead between his/her car and the charging point. Quod erat demonstrandum.

The OP stated in a previous post that he/she contacted the installer who advised him/her:
If you wish to use your charger to charge the car outside then regulations state the use of a TT earth is required, if the charge point is to be used inside then connection to your house earth is recommended

Whether or not the OP has any intention of charging his/her car outdoors is irrelevant. No provision has been made in regulation 722.411.4.1 for consideration of customers' wishes. What is of relevance, however, is that the regulation has not been complied with and has been breached by virtue of the fact that the installer has installed the charging point in a location where the point might reasonably be expected to be used to charge a vehicle parked outdoors. Quod erat demonstrandum.

The installer should have been aware of the inherent risks involved and acted accordingly by connecting an earth rod to the charging point therefore making this dedicated circuit a TT arrangement. The crucial point that I am making here is that locating an EV charging point indoors does not negate the need for an earth rod to be connected to the charger. That a charging point installed indoors can be used to charge a vehicle located outdoors necessitates a TT arrangement.

Subject to conditions (i), (ii) and (iii) of regulation 722.411.4.1 being satisfied, connection of an earth rod to a T-N-CS arrangement is permitted. However, we can immediately eliminate two of these conditions as plausible options. Since the OP's charging point is connected to a single-phase supply, condition (i) does not apply here. Given that it would be next to impossible to achieve the ultra-low Ra value that would be required to ensure that an open-circuit fault in the PEN conductor supplying the installation does not exceed 70 volts rms, condition (ii) is a non-starter. But condition (iii) can be satisfied by installing a charger that does not require connection to an earth rod. The Pod Point Solo is one such charger.

While regulation 722.413.1.2 permits the use of a fixed isolating transformer that complies to BS EN 61558-2-4 as a means of providing electrical separation for one electric vehicle supplied from one unearthed source, Mr. Smith and Mrs. Jones are not going to incurr an additional cost of several hundreds of pounds for an isolating transformer to be installed in their meter cupboard, assuming they had the physical space to accommodate the bulky transformer there in the first place.

So ultimately there were but two realistic choices open to whoever installed the OP's charging point: either install a charger that does not require connection to an earth rod, or install at least one earth rod to the charging point so forming a TT earthing arrangement for that dedicated circuit. Since the charging point that was installed in the OP's garage was not a model that would comply with the requirements of 722.411.4.1 condition (iii), the installer by default should have installed an earth rod and made the the earthing arrangement for that dedicated circuit TT. Quod erat demonstrandum.

Connections - Summer 2018.png

John Ward has produced an excellent and most informative video regarding the earthing arrangements for electric vehicle charging equipment. The segment between 10:25 and 11:09 explains the TT arrangements for a dedicated EV charging circuit. What JW says here is what I have been saying throughout this thread. So if I am wrong, then so too is JW. Is there anyone here who would like to step up to the plate and call him out along with the author of two articles that were published in Connections in June 2018 and in Professional Electrician in November 2018?


The installer of the OP's charging point also advised him/her:
Looking back at the information you provided, you requested that the charge point be installed inside the garage and we have assumed that this would be for the purpose of charging inside, we will look to clarify this to all customers going forward.

The assumptions of the installer are inconsequential. The requirements of regulation 722.411.4.1 are unequivocal, unambiguous, and perfectly clear. Crystal is opaque by comparison. A PME earthing facility shall not be used as the means of earthing for the protective conductor contact of a charging point located outdoors OR that might reasonably be expected to be used to charge a vehicle located outdoors unless any one of the three conditions attached to that regulation can be satisfied.

The photographs below are of an install that I recently completed in the garage of a local car-hire company. The earthing system is T-N-CS. There was no need for any earth rods to be installed in this installation as all three charging points are located indoors and are located in such a manner that they could not ever be used to charge an electric vehicle located outdoors. If there had been even the slightest possibility of the client ever using any one of these chargers for outdoor charging, then rest assured that I would have connected each charger to an earth rod and undertaken a risk-assessment in accordance with section 6.8 of the Code of Practice for Electric Vehicle Charging Equipment Installation and attached a written risk-assessment document to the Electrical Installation Certificate.

EV Charger 1.jpg

EV Charger 2.jpg

EV Charger 3.jpg

Main Board (a).jpg

The company who installed the OP's charger come across as being reasonable and approachable, The photos that the OP posted of the install indicate that it has generally been carried-out to a high standard. My advice to the OP, for what it;s worth, would be to ask the company to come back and carry-out a risk assessment with a view to converting the dedicated circuit for the charging point to a TT arrangement.

An alternative solution would be for the charging point to be replaced with a Pod Point Solo. However, given that the install was part-funded by grants from OLEV and the Energy Savings Trust, there would almost certainly be complications. But as things stand, the charging point in its present state cannot be left as it is because it does not comply.

I wish the OP well and trust that a satisfactory outcome will ensue. Please keep us posted of developments.

And on that note, I shall now exit stage left. I've stated my case and will make no further contribution to this thread.
 
Last edited:
Assuming one was to connect to a TT setup for that new EV circuit.
With regards to the risk-assessment in accordance with section 6.8 of the Code of Practice for Electric Vehicle Charging Equipment Installation....can I ask if there were any obvious issues shown in my recent photos of the garage area that would have highlighted a risk/problem?

Hence making this option of moving to a TT setup for the EV circuit not an applicable solution?

Apologies for my lack of understanding. But if there was the possibility of crossing PME earth with TT earth (ie TT setup indoor charger) Are my risk of hazard shocks still the same in the event of a supply fault (pen fault)?
 
From @JK-Electrical quotes;

"a PME earthing facility shall not be used as the means of earthing for the protective conductor contact of a charging point located outdoors OR that might reasonably be expected to be used to charge a vehicle located outdoors ..... "

Would I be correct in thinking that most domestic garages fall into the remit of the latter?
 
Apologies for my lack of understanding. But if there was the possibility of crossing PME earth with TT earth (ie TT setup indoor charger) Are my risk of hazard shocks still the same in the event of a supply fault (pen fault)?
Because your charger is located indoors (by the sounds) it needs to be the same earthing system as the house, which I understand is TNCS. But this is prohibited by regulation if the charger can be used outdoors.

Just thinking out loud - if the charger in the garage was TT but the nearby beer fridge was on a house circuit and the supplier lost neutral fault occurred, you’d have the fridge door handle at a high V and the car at zero V. This would present a significant shock hazard that your house RCD could not disconnect and the car / charger would nicely keep itself connected to E via the rod.

If your whole house, garage and charger were all TT and the same supplier lost N fault occurred then you would have no power, but you would be safe as N and E remain separated. Safe to get beer and touch the car :) .
 
Last edited by a moderator:
Thanks for confirming the hazards on the other way ie indoor charger TT earth setup, and where such supply fault occurs. Touch the car would cause shock hazard.

With that in mind I understand the risk assessment that was mention (section 6.8 code of practice of EV equip installs) would identify these possible hazards if they exist? Ie items in reach...
So with than in mind, my previous question asked was there anything obvious that one could see In the photos of the garage that posted previously that would highlight these types of issue? I appreciate this is not an assessment but just to help me understand if there was anything there that sprung to mind as an issue?
 
Thanks for confirming the hazards on the other way ie indoor charger TT earth setup, and where such supply fault occurs. Touch the car would cause shock hazard.

With that in mind I understand the risk assessment that was mention (section 6.8 code of practice of EV equip installs) would identify these possible hazards if they exist? Ie items in reach...
So with than in mind, my previous question asked was there anything obvious that one could see In the photos of the garage that posted previously that would highlight these types of issue? I appreciate this is not an assessment but just to help me understand if there was anything there that sprung to mind as an issue?
Hyeung, some of the posts above have mentioned TT. There are 2 different forms of this involved in the case of an electric vehicle charging point (EVCP). The case which is mainly being discussed is connecting an earth rod to the actual EVCP. This would be acceptable and meets the regulations. However, the regulations do not always take in to account practicality. There is absolutely no way this method will work for you as you would not need just one little earth rod, you would need multiple deep earth rods littered all around your garden, perhaps dozens, it would cost a fortune and is not practical.

The other option is to TT the entire garage, this is what I shall be doing for a customer soon (although now I am actually tempted to leave it as PME and suggest an EVCP that is suitable). However, their garage is 20m from the house so there is no chance of coming into contact with anything connected to the PME earth (e.g water pipes, gas pipes). With this form of TT only one earth rod will probably be needed.

With both options I think it unlikely you would get indoor charging as you have stated you have gas pipes in the garage. These will be simultaneously touchable with the car, thus introducing a potentially dangerous voltage (in the event of PEN break, ie a break in the neutral coming into your house).

The last option is to TT your whole house, you could then charge the car in or out of the garage without worry. However, this is really a step backwards with the earthing safety of your whole house as a PME earthing system is far better than a TT.

Realistically
your options are as follows, if you want to meet the regulations and avoid the one in a million additional risk.

1. Change EVCP for one that can be used with PME.
2. Ask company to move EVCP further into garage so it cannot be used outside.
 
Last edited:
I have a diesel car for sale...very economical, and can be "recharged" at thousands of points all over the world, in a matter of minutes, and each charge will take you about 500 miles.
Just saying...

It's the future.

5 words
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

hyeung

DIY
-
Joined
Location
Glasgow
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
EV Charger Installation - Cabling Query?
Prefix
N/A
Forum
Electric Vehicles Advice Forum
Start date
Last reply date
Replies
138

Advert

Thread statistics

Created
hyeung,
Last reply from
Jezeth,
Replies
138
Views
24,735

Advert

Back
Top