at high tide or low tide, that is the question.At a marina on a floating walkway or pontoon what height can you install a socket outlet?![]()
11x25x20/1000= 5.5v so complies but do i need todo anything for full load markie sparkie ... or anyone if you out there cheers markie sparkie you can mark now1) BS7617 is a non-statutory document, but if it is adhered to, compliance with which statutory document is likely to be achieved?
2) When may non-rechargeable auxiliary batteries be used in caravans?
3) With a DC voltage of 125V between conductors how would the installation be classified?
4) What is the most likely cause of an overload current arising in an electric motor circuit?
5) Under what conditions is the design current of a circuit defined?
6) Name a type of lighting equipment likely to require additional protection against thermal effects?
7) A component of a support system consisting of regularly spaced elements which mechanically retain a cable is defined as?
8) Name 3 SELV sources that will provide combined basic and fault protection?
9) A protective device giving protection to both overload and short circuit must be capable of breaking current up to what level?
10) A 230V single-phase heating circuit has a design current of 25A. The length of the PVC insulated cable is 20m. The 4mm[SUP]2[/SUP] cable installed has a volt-drop of 11mV/A/m. The voltage drop under full load conditions is? And does this comply with BS7671?
at high tide or low tide, that is the question.
I'm a little confused here;I've read this thread which was started by i=p/u , who i wholeheartedly respect on this forum, however what i can not fathom is this; are you doing a course on what i understand to be BS 7671 ? or are you doing the C&G 2391 ?
The reason i ask is, if you are doing 17th edition BS 7671, then this exam is open book, multiple question {(which means, an exam to show that you can read a book and find relevant answers to questions quickly in said book),The BRB soon to be The BGB}, where you should PASS with no less than 99% in your case. If however i read it at wrong, and you do indeed are doing the 2391, then pm me, as i have loads of help at your disposal.
Marnik
Minimum CSAs for flexes and cables for caravan connections I=P/U.......table and page no. please.......
2 methods of basic protection please I=P/U.........and one method of additional protection also.....
1 condom is basic protection. 2 condoms for additional protection.
do the 2391 as soon as poss. as the are about to change it. also while all regs are fresh in the memory, it should make it easier.
BTW the offer of help still stands!
2 methods of basic protection please I=P/U.........and one method of additional protection also.....
i am rude sorry readers
disconnection times for BS 61009/ BSEN 61009 please
Zs for BS 88
Zs for BS 1361
If you can answer questions like this, where you are given no clues, then you find the multiple choice of the exam child's play, easy peasy stuff.1= reg 114.1
Correct Reg, But which statutory document?
2= annex A the awnser lys but all i can say doesnt mention rechargable or not
Looking in the correct place, the answer is there in BRB.
3= part 2 defintions
Correct place, but what's the classification.
4= starting and stoping reg 552.1.1
Wrong.
5= part 2 definitions normal service
Correct.
6= luminaires marked D reg 422.3.2
Although not correct a good attempt, your thinking along the right lines, but I want a Reg associated with the specific thermal effects of luminaires, type of luminaire?
7= cable cleat part 2 definitions
Correct.
8= reg 414.2
Wrong Reg But close, Name 3 sources?
9= reg 432.1
Correct Reg, what current level?
10=
11x25x20/1000= 5.5v so complies
Correct.
but do i need todo anything for full load markie sparkie ... or anyone if you out there cheers markie sparkie you can mark now You already have the design current is the full load.
disconnection times for BS 61009/ BSEN 61009 please
table 41 0.4 TN systems and 0.2 TT syatem
What's the ratio of green / yellow colours on a CPC in percent?
Well done mate, I've added the answers to the two questions you struggled with to ease the agony.1= reg114.1 and electricity at work regulations 1989
Correct, also see Page 10 BRB Note from the HSE.
2= reg A721.55.3.1 only when independant from other supplies.
Correct.
3= part 2, low voltage
Correct.
4= cant find sorry.
Excessive mechanical load, Part 2, Definitions.
5= part 2, normal service
Correct.
6= extra low voltage reg 559.11.4
Wrong. Any luminaire radiant and/or convected heat source e.g. tungsten halogen security lamp. Reg 559.5.1
7= cable cleat part 2 definitions
Correct.
8= reg 414.3 (i) (ii) (iii)
Correct.
9= reg 432.1 upto pfc level where device is installed
Correct.
10=11x25x20/1000= 5.5v so complies
Correct.
soory for late response markiesparkie... never ride the day i saddle or im away without any shoes on..cheers