JanWilson

DIY
Reaction score
8
I have just had my house fully rewired. I lifted a few of the loose floorboards to clean and noticed at junctions there is a lot of exposed copper wire. Is this normal or even safe?IMG_20220120_184645_326.jpgī
 
Last edited by a moderator:
That is totally not good. First of all, in a complete rewire, there should not be any need for joints under the floor.
Secondly, any joints have to be made with all the terminals completely enclosed in a suitable box.
Third, the bare copper wires are circuit protective conductors and should be covered in green/yellow sleeving.

I would be seeking some sort of redress.
 
Exposed wires, should be housed in a joint box/ enclosure, choc blocks are dated wagos would be my choice, no sleeved earth conductors, my advice would be to get them back.
Is the company in an approved CPS (competent persons scheme)
 
totally unacceptable bodge. did they arrive on horseback? have you paid them in full? andwhat other horrors might there be lurking?
Thank you for your response, they have just sent out their invoice....... I found other areas similar. Can I ask, does a full rewire have to be passed by Building Control? and would it be standard to request they come and look at the job if I have concerns? Thanks so much for your help.
 
That is totally not good. First of all, in a complete rewire, there should not be any need for joints under the floor.
Secondly, any joints have to be made with all the terminals completely enclosed in a suitable box.
Third, the bare copper wires are circuit protective conductors and should be covered in green/yellow sleeving.

I would be seeking some sort of redress.
Thank you for your response, any advice is really helpful.
 
To expand. The bare copper is not correct but is not the most serious problem. The bare conductor is the CPC (earth) core and should be sleeved for identification purposes. However it is unlikely to be live or dangerous to touch. The first concern is that junctions between cables must be installed in suitable purpose-made enclosures, so that you only see the grey outer sheath of the cable entering, not the blue and brown cores nor the connectors joining them. Leaving those exposed is unacceptable as they are not mechanically secure nor protected against being touched.

'The second concern is that 'work' of that standard, as hinted at above, indicates a general disregard of both the regulations and accepted practice, even if it does not present an immediate threat to life. You just don't do it like that (although it's certainly not the first time nor will it be the last.) Also as mentioned above, hidden joints are undesirable and usually a sign of bad planning or damaged cables. They are often a sign of modifications to existing wiring; in normal circumstances they should not be found in new work, as there are usually better ways to arrange things so that all connections are made inside fittings where they are accessible.
 
Last edited:
To expand. The bare copper is not correct but is not the most serious problem. The bare conductor is the CPC (earth) core and should be sleeved for identification pusrposes, however it should not be live or dangerous to touch. But all junctions between cables must be installed in suitable purpose-made enclosures, so that you only see the grey outer sheath of the cable entering, not the blue and brown cores nor the connectors joining them. Leaving those exposed is unacceptable as they are not mechanically secure nor protected against being touched.

'Work' of that standard, as hinted at above, indicates a general disregard of both the regulations and accepted practice, even if it does not present an immediate threat to life. You just don't do it like that (although it's certainly not the first time nor will it be the last.) And also as mentioned above, hidden joints are undesirable and usually a sign of bad planning or damaged cables. They are often a sign of modifications to existing wiring; in normal circumstances the should not be found in new work as there are usually better ways to arrange things, so that all connections are made inside fittings where they are accessible.
Thank you, this is so helpful. I don't really understand electrical installations but as somebody who is used to seeing houses slightly deconstructed for refurb purposes this doesn't look as I would expect. Any further advice from anybody reading these threads is really useful. Thanks!
 
Thank you for your response, they have just sent out their invoice....... I found other areas similar. Can I ask, does a full rewire have to be passed by Building Control? and would it be standard to request they come and look at the job if I have concerns? Thanks so much for your help.
from the one photo you have posted, i have a mental image of the guy's that did this and it is not good.

did they have free reign to remove plaster etc. to drop cables to light switches and other fittings?

Before the invoice is paid, email them with a list of your concerns so far.
are they a member of a scheme like nappit or niceic? they should be otherwise they will find it hard to get part p of building regs adhered to.

did you have any form of quote for the work detailing what was to be done and for how much?

from the single picture it is clear that they have not adhered to the letter or the spirit of the regulations
some more pictures would be great and the collective team will let you know just how bad it is.
 
from the one photo you have posted, i have a mental image of the guy's that did this and it is not good.

did they have free reign to remove plaster etc. to drop cables to light switches and other fittings?

Before the invoice is paid, email them with a list of your concerns so far.
are they a member of a scheme like nappit or niceic? they should be otherwise they will find it hard to get part p of building regs adhered to.

did you have any form of quote for the work detailing what was to be done and for how much?

from the single picture it is clear that they have not adhered to the letter or the spirit of the regulations
some more pictures would be great and the collective team will let you know just how bad it is.
Thank you James. I will post more pictures tomorrow. I have just finished clearing up after eight days of mess and in answer to your question, yes, sadly they have removed plaster, dropped wires and replaced everything. I bought my childhood home from my mother who had to go into a home as she has dementia - they knew this. I feel as though they have wrecked her house. Very sad.
 
For the time being, DO NOT PAY THE BILL.

I have a horrible feeling that when we see the rest of the pictures the advice may well be to involve trading standards.
If they are a member of a scheme then there should be some redress available from them.

We await your next batch of pictures and hope that it is not as bad as i fear it may be.
 
New posts

Reply to Exposed copper wire under the floorboards after rewire in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
780
Looking for opinions on this guys.... I visited a rewire on a bungalow, classic build, a concrete floor slab with gap above then floorboards ( the...
Replies
7
Views
2K
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
So I just started out recently and I’m struggling with what to price myself at. It’s worth noting I live in the east London area and I’m looking...
Replies
12
Views
532
Had a floorboard up recently following a water leak. While there, thought I would connect in a stair light, which previously was switched...
Replies
2
Views
737

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock