Customer wants to take power from an existing garage (with board) to supply a greenhouse, to be fitted with ip rated switchgear.
The greenhouse is made of aluminium.

Since this is an extraneous conductive part am i right in thinking that the aluminium frame would require a 10mm bond at least? (tncs supply)

Garage is fed with a 4mm armour (3core)

Should i still take the supply from the garage but run in a seperate 10mm earth from the house MET?
 
What's being put in the greenhouse? Maybe an IP rated outlet just outside it would allow use of garden tools etc.
 