Right that makes perfect sense, thanks.

But, as ive already said, (to much hilarity) the greenhouse is not on a plinth, so why would this apply?
Am i missing something here? (apart from a brain)
 
Right that makes perfect sense, thanks.

But, as ive already said, (to much hilarity) the greenhouse is not on a plinth, so why would this apply?
Am i missing something here? (apart from a brain)
Because the concrete plynth may offer more insulation resistance against the path to earth, than if the metal frame was in direct contact to the earth. Just test the frame as already been mentioned if its greater than 25kohms (a safe bet value) then it would not be considered extraneous. But if you find that the tested value is very close to the minimum accepted value (22kohms) and environmental conditions might reduce this value further then its your call.
 
so what about, i take the tncs supply from the garage (2.5mm 3 core armour). This would supply earth to all of the circuits only. And then seperatley i connect a 10mm earth onto the greenhouse frame and then into a earth rod?
 
No good I'm afraid.
By earthing the frame with a local rod you ensure it is an extraneous conductive part and so needs connection back to main earth terminal. Or TT'ing. See @davesparks post #19 :) .
 
basically im trying to get out of digging a trench back to the house (many reasons).

But my other problem is that inexperienced with "tt ing" something.
So im just supposed to run a live neutral from the garage (unearthed) to the greenhouse, then stick a 30ma board/earth rod.

or do i earth the armour at the garage side but leave the greenhouse side unconnected to its respective earth terminal.
 
or do i earth the armour at the garage side but leave the greenhouse side unconnected to its respective earth terminal.

yes. earth armoured at supply end. TT the greenhouse. bond the metal frame if required.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Glasgow

Thread Information

Title
Extraneous Parts Earth sizing
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
Neon Vagabond,
Last reply from
Neon Vagabond,
Replies
24
Views
4,059

Advert

Back
Top