Fault finding on ring final, is this the readings you would expect to achieve and are these the correct way to find them thanks

1568C8E7-FCD1-4450-AE68-637CDA06B574.jpeg


10A5C758-49EA-4891-9684-94ED5F9EDC04.jpeg
 
3rd year apprentice don’t do much fault finding
Then to aid us in helping perhaps you could update your profile and avoid unnecessarily obtuse answers.
If you are in training then I suggest you apply for access to the trainee area, lots of help on there from Mentors me included.
 
I don’t fault find at work so pointless asking my boss and it’s for AM2 in few weeks and college have too many people to bother about showing me
Have you looked at the video yet? that should help know end, not much of a Boss if you feel you can't ask him a question, decent people won't mind answering a legitimate question. Where are you based? Sorry missed that London too far for me to come and help you out.
 
Have you looked at the video yet? that should help know end, not much of a Boss if you feel you can't ask him a question, decent people won't mind answering a legitimate question. Where are you based?
Yes I’ve watched it, just wanted to know as in AM2 your only allowed continuity tester so all faults are wiring it’s just the same as dead testing just wanted to know if my drawings was correct
 
Seems odd to me that they only allow a continuity tester, the correct way would be to get resistance readings r1 r2 and rn and then do a figure of 8 R1+R2 reading that would prove your RFC is complete and OK.
 
Pete's approach above is the best one, it will catch most faults, but as you only have a continuity tester:
Reverse polarity:
Normally easiest to find by inspection.
Assuming you have correct end to end resistance results, Joining two poles at the board one of which is not the expected reversed polarity and testing at the socket fronts should give one socket with OL result all others should be very low resistance.
Your diagram and method will work.

Open circuit:
discovered by end to end testing, join one non continuous core to a continuous core and test between the cores at each socket, when you get OL result this is where the fault exists (or the socket beforehand on the outgoing core).
Your diagram and method will work so long as only one leg is joined.

High resistance:
Similar method to open circuit but where the resistance rises is where the fault is (or the socket before hand).
Your diagram and method will work.

Short circuit:
testing between disconnected cores at board the low resistance reading indicates the faulty cores, break the ring down half and half again testing each time between the faulty cores until the fault is narrowed down.
Your diagram and method will not work. only the bit about breaking the ring applies, adding another short circuit to the circuit will not help.
 
Pete's approach above is the best one, it will catch most faults, but as you only have a continuity tester:
Reverse polarity:
Normally easiest to find by inspection.
Assuming you have correct end to end resistance results, Joining two poles at the board one of which is not the expected reversed polarity and testing at the socket fronts should give one socket with OL result all others should be very low resistance.
Your diagram and method will work.

Open circuit:
discovered by end to end testing, join one non continuous core to a continuous core and test between the cores at each socket, when you get OL result this is where the fault exists (or the socket beforehand on the outgoing core).
Your diagram and method will work so long as only one leg is joined.

High resistance:
Similar method to open circuit but where the resistance rises is where the fault is (or the socket before hand).
Your diagram and method will work.

Short circuit:
testing between disconnected cores at board the low resistance reading indicates the faulty cores, break the ring down half and half again testing each time between the faulty cores until the fault is narrowed down.
Your diagram and method will not work. only the bit about breaking the ring applies, adding another short circuit to the circuit will not help.
Thanks so open circuit connect at board end eg. L+N then test at socket between L+N if I get reading OL then open circuit or can do end to end on each socket eg test L to L from socket 1 to 2,
Short circuit, so break ring in half then test end to end at each socket no r1+r2 as this is just adding another short circuit
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Fault finding on ring final circuit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
35
Unsolved
--

Advert

Thread statistics

Created
Bradley6969,
Last reply from
static zap,
Replies
35
Views
13,232

Advert

Back
Top