Discuss Feeding 250 amp 3 phase board direct from buzz bar need isolatir in the Commercial Electrical Advice area at ElectriciansForums.net
Yes I have to agree, you need to have a chat with your boss and explain that at the moment this maybe outside the scope of your competence and you need some guidance and assistance. I think you may also need to bear in mind that he, assuming it is a he has not really thought this through. This isn't routine domestic work as you have realised and the reality from a piece of paper can be a harsh lesson.
Thx for constructive advise darkwood hence why I'm querieing the design.
So could I come straight off the bus bar into dist-board and double up the tails?or will I need to replace the main switchwith a fused switch aswell? Thx
You can come direct from the busbar but your conductors need to be at least 95.0, have you ever worked with this size of conductor.
Yes I have to agree, you need to have a chat with your boss and explain that at the moment this maybe outside the scope of your competence and you need some guidance and assistance. I think you may also need to bear in mind that he, assuming it is a he has not really thought this through. This isn't routine domestic work as you have realised and the reality from a piece of paper can be a harsh lesson.[/QUOTE
If the isolator feeding the busbar has 100amp fuses in could I then feed the dist board directly with 35 mm tails and downrate the dist-board switch to a 100amp mccb.
If my boss is adamant about using the isolator I will still need to use 35 mm tails anyway is that right ?
Thx for advise
Yes you could although the main switch at the board is not likely to be an mccb but an EN60947-3, 125A isolator.
So downrate the the dist- board switch to 125. Amp?
If he's adamant about not changing the isolator or dist- board all I need to do is feed the isolator with 35 mm tails which feeds the dist- board with 35 mm tails which don't route through the bus bar chamber as long as the fuses feeding the bud ad are 100amp
Sorry earlier I'm sure you said the busbar was fused at 200amp, now are you saying 100amp? It changes alot of the advice or are you suggesting derating them which is unwise as it strangles the future use of the busbar plus you need to assess the demand existing.
Reply to Feeding 250 amp 3 phase board direct from buzz bar need isolatir in the Commercial Electrical Advice area at ElectriciansForums.net
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Deleted member 155212
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K