freedomrun

If faced with a Domestic Final CCT (Lighting or S/O) and it has 2 sizes of T&E used, lets say a lighting CCT with 1.0mm used on some lights and 1.5mm used on other lights and if Zs & IR all complies - When writing out the Schedule of Test Results, what size Wiring conductor should be noted in column 4? Or should a remark be made in column 15 against this CCT stating that two sizes of cable are in the circuit. My question is really aimed at Lighting CCT's, but i guess two sizes of T&E are also found in S/O final CCT's now and again. Any ideas with regard to completing the Schedule of Test Results in relation to this please? Thanks in advance.
 
Personally, I would probably write 1mm (being the lesser), but I suppose a note wouldn't do no harm.


When I was an apprentice working for a biggish firm (mainly office refurbs), they would often take 4mm from the board to the the first sockets and then 2.5mm to finish off the ring, which made sense (cos of volt drop and Zs), but it wasn't until I left and started filling in the certs that I thought what did they used to put on their certs.

There should be more room on certs!
 
I understand it quite common for lighting ccts to have the switch drops wired in 1mm2 but the loop in/out in 1.5mm2
 
i used to do the swith drops in 1.0mm, especially 2 way switching and the loop in 1.5mm (assuming calcs fine) and then put 1.0 on the cert as you need to make sure the circuit is ok for worst case. tend to use 1.5 on all now (except 2 way) to save on stock holding.
 
i used to do the swith drops in 1.0mm, especially 2 way switching and the loop in 1.5mm (assuming calcs fine) and then put 1.0 on the cert as you need to make sure the circuit is ok for worst case. tend to use 1.5 on all now (except 2 way) to save on stock holding.
same here, but usually 3 core+cpc is in 1.0mm, so strappers are in 1.0mm. if strappers and switch wire are in 1.0, i generally put the loop wiring ( 1.5) on ther cert, as the switching cables carry the load for only one light. also, one advantage of wiring switch drops in 1.0 is easy ID of switch wire when 2nd fixing ( laziness really)
 
Last edited:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Final CCT's with 2 sizes of T&E fitted
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
freedomrun,
Last reply from
telectrix,
Replies
4
Views
1,593

Advert

Back
Top