Hi all,
I have a single switch in my garage to turn on a couple of lights in there. Yesterday I fitted a floodlight outside, drilled through garage wall and fed the cable inside and fitted a 2 gang switch so the floodlight had its own. I 'nicked' the power inside the switch via a loop from com to com to feed the floodlight but am not getting the full power to the floodlight. It's a 50w LED and I have a CU in the garage that protects the sockets and lighting. Any idea as to why it's not getting full power please. Regards
 
Can you show a pic of the switch I suspect you don't have a neutral.
 
Can you say where the brown, blue and earth are connected at the switch.
 
Brown connected to com along with the brown from the switch next to it to take the power from that com. Blue into L1 so as to make the switch work as it is on the other switch and the earths are all joined and connected to switch plate. I also ran an earth link to the back box as the switch is metal
 
There is no neutral at that switch. The brown and blue of the existing cable are both lives, live in and live out. The blue should have a brown marker on it to indicate this.
 
There is no neutral at that switch. The brown and blue of the existing cable are both lives, live in and live out. The blue should have a brown marker on it to indicate this.
Yes I did have a brown sheath over the blue you're right. The right hand side is existing lights in the garage which are working fine and I have not changed. The black cable on left is the new floodlight cable. I will replace the brown sheath. This should then go into L1 to make switch work?
 
Unfortunately you don't have a Neutral at the switch position , they original installer has 3 plated at the light or you have a JB ( junction box ) somewhere in the rafters.
Its unusual these days not to have N at the switch especially in newer builds.
You are unfortunately going to have to bring a N down to the switch to make the flood light operate
 
Yes I did have a brown sheath over the blue you're right. The right hand side is existing lights in the garage which are working fine and I have not changed. The black cable on left is the new floodlight cable. I will replace the brown sheath. This should then go into L1 to make switch work?
I don't understand why I'm not getting enough power from the second switch as I've looped in to feed the floodlight from switch
Unfortunately you don't have a Neutral at the switch position , they original installer has 3 plated at the light or you have a JB ( junction box ) somewhere in the rafters.
Its unusual these days not to have N at the switch especially in newer builds.
You are unfortunately going to have to bring a N down to the switch to make the flood light operate
Thanks for all the replies. Penny just dropped! Of course need live in & out. Thanks again..
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician
If other, please explain
I have completed a domestic installer course
Business Name
Treadstone Electrical Ltd

Thread Information

Title
Fitting outside floodlight
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
13

Thread Tags

Advert

Thread statistics

Created
Le Bren,
Last reply from
Le Bren,
Replies
13
Views
2,071

Advert

Back
Top