714gold714

Hello there basically i rewired a 3 bedroom house about 9 months ago tested out fine and have had no problems at all.

However received a phone call today from customer saying that all power has gone off, arrived and found that on the dual RCD board i fitted i would switch on the shower circuit (switch on at button on shower) which is powered by the 2nd RCD and switch on the 1st RCD powering kitchen lights it will trip the 1st RCD. In the end i totally disconnected the kitchen lights and the shower worked perfect and all the other circuits but as soon as the kitchen lights are connected it trips.

The circuit is not being over loaded as i have done a clamp test etc

Also when I had the kitchen lights on if i plugged anything into the sockets it would trip, it just seem as soon as a load is applied with the kitchen lights on it trips.

I have had done insulation resistance but my tester was playing up im going to do insulations tests tomorow with my new tester.

Also customer said that they changed one of the bulbs in kitchen ( 12 downlights ) as when it first started the rcd had tripped

Please help lol just cant get my head around it
 
have you done the new IR test yet ?, are there any fans, outside lights spurred of the kitchen lights ?
 
Maybe the heat from the lights have damaged the cables and this is the issue. As for the shower I don't quite understand what you've written!
 
thanks for replys i have a bad feeling its the kitchen lights there is x12 240v GU10 downlights soon as these are connected in circuit it plays up with everything. will IR soon as i find a replacement. Sorry about desciption very hard to describe
 
No spurs etc off lights i ran a dedicated circuit for kitchen lights strictly for downlights
 
Not quite following original post and had a few strongbows but could it be a neutral in wrong neutral bar??
 
Hello there basically i rewired a 3 bedroom house about 9 months ago tested out fine and have had no problems at all.

However received a phone call today from customer saying that all power has gone off, arrived and found that on the dual RCD board i fitted i would switch on the shower circuit (switch on at button on shower) which is powered by the 2nd RCD and switch on the 1st RCD powering kitchen lights it will trip the 1st RCD. In the end i totally disconnected the kitchen lights and the shower worked perfect and all the other circuits but as soon as the kitchen lights are connected it trips.

The circuit is not being over loaded as i have done a clamp test etc

Also when I had the kitchen lights on if i plugged anything into the sockets it would trip, it just seem as soon as a load is applied with the kitchen lights on it trips.

I have had done insulation resistance but my tester was playing up im going to do insulations tests tomorow with my new tester.

Also customer said that they changed one of the bulbs in kitchen ( 12 downlights ) as when it first started the rcd had tripped

Please help lol just cant get my head around it
well for a start whats overload got to do with an RCD?...
 
thats what i originally thought with neutral in wrong bar but its been working fine for 9 months solid with no faults or trips at all
 
i suspect damaged cables on kitchen light circuit causing a N/E fault. dis. the kitchen light circuit from CU ( all 3 conductors) try a continuity test N-E. if reading is > 10k ohms, then IR test N-E.
 
just trying to borrow a IR tester.

It is a complete head scratcher, he also said aswell when he canged a bulb in the downlight it didnt come on at first and he wiggled the cable and it came on so I wonder if hes pulled a connection out in junction box in the floor
 