I'm with you all the way, apart from 101.19/115 equaling 10.05. I feel awful for pointing that out.Easy method, use the adiabatic equation to find out the size
S = ✓ I^2 * t / k
I = the current required to operate the device
t = disconnection time required for the device
k = factor given for the cable selected - Typically 115
So for argument's sake, let's say we have a fault current of 320 (taken from your trip curves) a time of 0.1 (taken from your device operating times) and a K factor of 115 (taken from the tables following the trip times)
S = ✓ I^2 * t / k
S = ✓ 320^2 * 0.1 / 115
S = ✓ 102,400 * 0.1 / 115
S = ✓ 10,240 / 115
S = 101.19 / 115
S = 10.05
As there is no conductor with a CSA of 10.5, you select the next size up, in this case 16mm^2
The above is purely and illustration and values may not be accurate but it serves to show how to lay out the equation so that you can understand what is going on at each step.
Hope this helps
Don't, the point was to put across the layout/concept, thr fact that maths is wrong just gives me a chuckle.. that'll learn me for trying to be a smartarse ?I'm with you all the way, apart from 101.19/115 equaling 10.05. I feel awful for pointing that out.
Sorry
Drop a PM to @Dan or @Lou , follow the template given and you'll be in soonHi guys, new to the forum. Can some one tell me how I can get access to the trainee forum? Everytime I click on the link Apply to Gain Access to Trainee-Only Forum, it stays on the same page.
I'm probably just being a bit thick!
Thanks for the help lister! Think I have nailed questions 1,2,8,9,10. Going to give the others a shot now but will be back if I need some hints/tipsMost listed here; Electrical Symbols | TLC Electrical - https://www.tlc-direct.co.uk/Technical/Symbols/Index.htm
In fairness you'll find that ones you need in OSG, atypically you'll be using sockets, light fixtures, light switches, motors, emergency lighting and the standard symbol for a CU
Hi on question 1 did you find an example on the internet to useThanks for the help lister! Think I have nailed questions 1,2,8,9,10. Going to give the others a shot now but will be back if I need some hints/tips![]()
Likely yes, it's not a hard one to grasp; Find a manufacturer (Fusebox, Wylex, BG), Download/Print the datasheets and use them in your project. Not sure why this is hard for some (not a dig at OP, purely an observation as it's not that first time this has come up)Hi on question 1 did you find an example on the internet to use
Are you on Q4? What distribution circuit?Hi all, doing my design assignment. Ive done questions 1,2,3 and filled out table 1 as best i could. When it comes to the distribution circuit, im a bit lost. I know it needs a 5s disconnection time but apart from that is there another calculation i should be doing? Also what type breaker should be feeding it? Thx for any help
Yes I’m stuck on question 4 if you can helpAre we still doing this guys? I am and can help out if you need it.
what is question 4? can't answer it without knowing the details, i honestly have no idea how anyone found this part of the course hard. the science exams and equations were by far and away the hardest parts of the course, the rest was like an English comprehension exercise.
I tend to agree with you, there.God I hate the grey-out on this forum, I use browsers with built in ad-blockers and I won't be changing this in the foreseeable future. No other forums I'm on do this --------, so I won't be making any exceptions for this place! You've got a strip of adverts down the right hand side of the screen and that should be enough to keep you ticking over, now I realise why I stopped coming to this forum!
@John J I can't PM you as you have limited who can see your profile.
PM me & I'll send you my PDF file
@John J I can't PM you as you have limited who can see your profile.
PM me & I'll send you my PDF file
Do you still need help?Hi Loki,
I’m also on this part of my 2365 and am very stuck. Would you mind sharing your pdf’s with me? A heads up would really be appreciated.
Best wishes
RS
Hi John hope you and family are well have you done you designSo I’ve recently started my level 3 course and I’m doing electrical system designs the one with the hotel extension and pool and cafe block I’ve done question 1 but stuck on all of question 2 some guidance would be appreciated thanks.
Hi John hope you and family are well have you done you design
Hi,
Your training provider should give you a template form?
Here's what we were given.
HI , IF IT POSSIBLE SEN ME YOUR PROJECT FOR HAVE A LOOK , PLEASE?Hi,
Your training provider should give you a template form?
Here's what we were given.
HI , IF IT POSSIBLE SEN ME YOUR PROJECT FOR HAVE A LOOK , PLEASE?
YES, HE DID, BUT I AM CONFUSED FOR THE FILLED FORM, I NEED A SAMPLE FOR UNDERSTANDING, THANKSHi,
Your training provider should give you a template form?
Here's what we were given.
No, by this point you should have sufficient knowledge and be able to search and reference texts. If you require guidance it can be given but this is all about the appliance of knowledge.Am I missing something here on these courses are they not supposed to teach you something followed by you use this learning and use it to complete the project?
I've given up responding to requests like these now, especially when you check how long they've been a member here.No, by this point you should have sufficient knowledge and be able to search and reference texts. If you require guidance it can be given but this is all about the appliance of knowledge.
No one in their right mind is going to do 4 years work and hand it to you so you can copy it. Certainly not me anyway. If you have a question attempt it, post your answer and we can help from there.YES, HE DID, BUT I AM CONFUSED FOR THE FILLED FORM, I NEED A SAMPLE FOR UNDERSTANDING, THANKS
So I’ve recently started my level 3 course and I’m doing electrical system designs the one with the hotel extension and pool and cafe block I’ve done question 1 but stuck on all of question 2 some guidance would be appreciated thank
Did you manage to get this assignment done?So I’ve recently started my level 3 course and I’m doing electrical system designs the one with the hotel extension and pool and cafe block I’ve done question 1 but stuck on all of question 2 some guidance would be appreciated thanks.
What do you need help with?Did you manage to get this assignment done?
I’m in the same position, some help would be appreciated, if you get a cance can you message me, thanks
Hey I'm due to start this module at the end of next month I was wondering if you had a link to these questions so I could get a head start on what to expect thank you in advance
Hi mate, did you complete your 305 assignment?Can you send to me the drowning please