high ze

Discuss high ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

evening
carried out a p i r today and the ze was 0.45 on a tn-s which i know is higher than it is meant to be.
i would like to quote a reg in the report but cant find it , help anyone please?

That's fine for TN-S.

Also, it's not in BS 7671 as it is supply so really comes under ESQCR 2002.
 