Hi All,

When connecting a motor, how do you know whether it needs to be wired as star or delta?

Thanks
 
It depends on what it is you want the motor to do.
If the output torque when wired in star is sufficient for the job you want the motor to do, then it can be wired in star.
If it is insufficient, then it will have to be wired in delta.
If the output torque required is so great, that the start up current will cause an overcurrent, then you will have to use a star/delta starter.
This allows the motor to be started in star, and when the motor is running at ideally 75-80% of the delta speed, contactors change the wiring configuration from star to delta.
 
Check the rating plate. It will give the voltage and connections, some will give two voltages.
400V Star
220V Delta

If it shows 400V Delta them it is suitable for star / delta starting.

It is inefficient to run a 400V delta motor in star
 
Thermal or electronic set at 100%
Dash pot 115 to 125% but you have to know how to set the time lag.
 
Last edited by a moderator:
Dash pot 115 to 125% but you have to know how to set the time lag.

Geezus, ....I haven't seen an oil dash-pot motor Overload unit for god knows how many years now!! Do they still make them Tony??
 
Yes, get in to the old heavy stuff and it’s still there. It’s like me and you, old but works when needed.

It’s one thing I’m dreading in starting the “Motor” sticky in this forum. I’ve got to get my brain back in gear
 
As with everything within industrial electrics, wire as per manuf. instructions. In this instance the motor plate tells you almost everything you need to know. You need to know what supply characteristics you're applying to the motor you have. If you have a 3 phase 400Vac supply and a DOL starter then the plate tells you to connect it with respect to the ratings.
MotorPlate.jpg
 
Tony

I have numerous relevant photos that I've taken for the App. Program. Motor plates and connections.

If you want them PM me and I can forward them on.
 
also come across 400/660V or maybe 415/690V or something similar a few times (the most recent 2 week ago), you wanna connect that as per Delta when using a 400V supply.
 
12-18 months ago I carried out a maintenance check on a bottle inspection machine and declared a motor, in a wet area, needed monitoring due to low(ish) IR reading. This is the original's plate.

SDC106872.jpg


It caused a little confusion. The hierarchy decided to get in a 3000rpm 50hz model and have it fitted to allow the original to go for overhaul. The machine would not run correctly due to obvious speed differences!
 
Last edited by a moderator:
Hmm, that’s a novel one to have thrown at you. Where the hell did it come from in the first place?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
How to know whether to wire as star or delta?
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
whazza22,
Last reply from
Knobhead,
Replies
14
Views
36,227

Advert

Back
Top