B

bs7671

Hi there my question is if you were installing a final circuit in a computer room for IT purposes,how would you wire the c.p.c.I think maybe it is something to do with a switchmode something or two earths???I have looked but cannot find anything specific to answer this.Help appreiciated thanks guys n gals
 
unless it is specifically stated that earth free sockets are required, I would wire them normally. What do others think
 
The NIC told us that for IT equipment and areas using computers you need to use sockets with two earth terminals and connect each cpc seperately. Also at the distribution board the two cpc's from your ring need to be terminated in seperate terminals on earth bar. Not sure what reg number was tho.
 
It is because of the potential for high earth leakage on IT equipment....the regs are to ensure that each outlet will maintain a cpc connection even if one cpc becomes disconnected. The cpc's must be run as a ring whether the circuit is a ring or radial and each cpc must be connected to a separate terminal at each socket and at the DB.
 
Just throwing one in here but if the earth positions are already marked by manufacturer, and the rest are full how do you do seperate earths in CU. Crimping makes the 2 ends " one conductor" ( I think). Could they then go into the same point on the earth bar?
 
excellent answer, wirepuller. clarified the post exactly. as to jeremy's post, wouldn't it be a good idea for CU manufacturers to add a couple of extra holes in the earth bar, for this very purpose?
 
What you are permitted to do is this.

CPC 1 from circuit 1 in terminal 1 along with CPC 1 from circuit 2
CPC 2 from circuit 1 in terminal 2 along with CPC 2 from circuit 2 etc etc.
Using this method takes up no extra ways on terminal block. This is only acceptable if the CPC's are all marked with their correct circuit number and the cu is labeled accordingly.
 
and, whatever happened to the removable earth link so one could split the main earth to get Ze. only reason i can think of is if some careless sod left it off, but same careless sod could leave the earth cable out. either way would show up when Zs readings were taken
 
What you are permitted to do is this.

CPC 1 from circuit 1 in terminal 1 along with CPC 1 from circuit 2
CPC 2 from circuit 1 in terminal 2 along with CPC 2 from circuit 2 etc etc.
Using this method takes up no extra ways on terminal block. This is only acceptable if the CPC's are all marked with their correct circuit number and the cu is labeled accordingly.
i can see the reasoning behind it but it seems a bit trusting of those following?
 
As long as the guy following is competent enough to know about high integrity earthing then there shouldn't be a problem. If he isn't competent he shouldn't be near it.
 
I can see this becoming a general requirement in the forseeable.....the justification being the ever increasing use of IT equipment in the home......probably worded 'any circuit supplying socket outlets which may reasonably be expected to supply an item of IT equipment'....which of course would mean an amendment...all buy another regs book,guidance notes,courses......DOH!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
How to wire cpc in class rooms
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
26

Advert

Thread statistics

Created
bs7671,
Last reply from
Sintra,
Replies
26
Views
4,521

Advert

Back
Top