That's actually how I was taught and what GN3 appears to say; Julie's logic and reasoning is spot on, and in this case I might have done it anyway to help build a picture of what is going on.

No argument about the logic/reasoning. I'm also mindful that GN3 implies that in all circumstances where you have live final circuits (required for these tests) you should have the bonding connected. But it also doesn't specifically describe the Zdb test as far as I can tell.

It only seems to discuss two cases - testing external earth loop impedance with main earth disconnected, and all other earth loop impedance tests where it says that "for safety and practical reasons neither the connection with Earth nor bonding conductors are disconnected". (Page 66)
So while I think it might have been a handy test to do I wouldn't say the OP is doing it wrong either.
That's really why measuring R1+R2 dead, and calculating zs from the ze/zdb + the measured circuit loop resistance is the usual practice, it allows you to obtain the minimum zs whilst not exposing users to an un-bonded system.
 
by disconnecting main bonding conductors to water and Gas?
Exactly.

Just as @Julie. says when you have the bonding in place you might have parallel paths lowering the supply's R2, hence you might see a much higher PFC and that is something to take in to account when verifying that OCPD is able to safely interrupt it.

However, such parallel paths are not guaranteed to remain. So if someone replaces some of a metal water pipe with plastic you might lose a parallel path and so the only safe assumption is the supply earth is there for faults. So checking Ze allows you to check that under a change of bonded part(s) you are still able to disconnect fast enough under fault conditions.
 
Yes, typically the only way to measure Ze is to isolate the installation supply (usually via the incoming switch) so it is completely dead, and then disconnect the supply earth and measure to it, and put it back immediately. Removing the bond conductors might do it, but as you can have links from the installation CPC to extraneous metalwork via boiler CPC, immersion heater CPC, or supplementary bonding, etc, you can never be sure.

Measuring Zs is simpler as everything is still in place. Of course if the supply earth is faulty then you would risk raising the CPC and any extraneous parts with a high impedance to potentially dangerous voltages, but most MFT will usually throttle the test current if they see a voltage change that could exceed 50V to keep things reasonably safe.
 

Reply to I am getting very high zs readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
863
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock