Looking at the photos would indicate that section 714 applies - Outdoor Lighting Installations, which also includes highway power supplies and street furniture.

714.411.2.201 Provisions for basic protection -
The enclosure must have an IP rating of at least IP2X.

714.512.2.105 Electrical equipment shall have, by construction or by installation, an IP rating of at least IP33.
 
Except the client is insistent it does not need an IP enclosure inside the metal cabinet, they insist it is fine as it is and to just go ahead and install, we will be instructed to install to the cabinet. So yes 16 posts on and some pictures the question remains the same, are they in breach of a regulation by deciding to not use a proper IP rated cabinet? Feel free to say you don't know, if you don't know.
So you clearly believe there is a reg so have you looked at all the various regs other than the BS7671 book relating to IP ingress for an answer?

From a quick look at the BS7671 regs Appendix 1 lists BS EN 60529:1992 +A2:2013 and that references Appendix AD2 with regard to water ingress

May be you need to do some tests with the enclosure and mast setup and spray some water from a hosepipe on it and at it and see what water ingress you get. If your client has other similar setup's installed some time ago maybe you need to get the clients permission to inspect a few to ascertain if there has been any water ingress, any degradation of the equipment has occured and the suitability of the setup for the application you have
 
When the IT products (that are going in this) were designed, they were designed to meet (probably ISO/IEC) product standards, to gain approval from an accredited test house - CE marking and all that! The MI's should specify if the product is IP rated, and if so what rating. If IP rated, compliance would be tested by the test house as part of product approval.

I would expect this platform side mast/box combo to be similarly designed to meet necessary standards. If not ISO/IEC etc, maybe Network Rail or whoever have their own standards. I find it surprising that there doesn't appear to be a specification for this platform box - that is where the IP rating would typically be found.

The correct design and construction of this thing should be lead by the applicable (generic) product standard, and/or the client specification. As mentioned by UNG, this is where I would expect IP requirements to come from, not our wiring regulations.
 

Reply to Install LV Network Switch and Patch panel in outdoor non IP rated enclosure in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock