Hi Guys
I have just passed my 2391 after a 4 week course and my background is in the installation of Digital TV Systems, predominantly Integrated Reception Systems which deliver satellite and terrestrial signals to blocks of flats, etc.
The reason I am posting on the electrical forum is I am in the middle of a huge debate over the use of earth electrodes (or "spikes" as my colleagues call them!).
The TV industry is regulated by the Confederation of Aerial Industries (CAI) who state you must install a supplementary bond back to the MET of the building to make the TV System electrically safe.
This is all well and good in blocks of flats which have a communal landlord supply, but many of the blocks I am upgrading are nothing more than rows of bungalows which do not have an MET as such, rather there is an MET in the CU of each bungalow/flat.
Its usually impossible to access any of these properties at the time of install and the customers are reluctant to have you route a 4mm2 earth cable into their CU anyway, so the "solution" according to many is install an earth spike.
The earth electrodes are being installed by non electrically qualified individuals, not tested and are literally drilled into the concrete or jabbed into the grass and then a lug is used to connect the 4mm2 earth cable to the electrode, forming the supplementary bond, no mechanical protection or anything. Not to mention running the risk of hitting services such as gas and water pipes, etc.
I understand the resistance of an earth electrode must be under 200 ohms, this isn't checked most of the time and when it is I usually find that several earth electrodes have to be daisy chained together in order to reduce resistance under 200 ohms.
The CAI state that the resistance of the outer conductor of the coaxial cable to the MET must not exceed 4 ohms.
Is it just me or does anyone else see an issue here?
I've always had trouble getting my head around the need to earth bond TV systems, I understand that by running coaxial cables to each property in a block of flats you essentially create an electrical circuit that needs to be made safe buy typically the max voltage you are working with is 18V.
I have just passed my 2391 after a 4 week course and my background is in the installation of Digital TV Systems, predominantly Integrated Reception Systems which deliver satellite and terrestrial signals to blocks of flats, etc.
The reason I am posting on the electrical forum is I am in the middle of a huge debate over the use of earth electrodes (or "spikes" as my colleagues call them!).
The TV industry is regulated by the Confederation of Aerial Industries (CAI) who state you must install a supplementary bond back to the MET of the building to make the TV System electrically safe.
This is all well and good in blocks of flats which have a communal landlord supply, but many of the blocks I am upgrading are nothing more than rows of bungalows which do not have an MET as such, rather there is an MET in the CU of each bungalow/flat.
Its usually impossible to access any of these properties at the time of install and the customers are reluctant to have you route a 4mm2 earth cable into their CU anyway, so the "solution" according to many is install an earth spike.
The earth electrodes are being installed by non electrically qualified individuals, not tested and are literally drilled into the concrete or jabbed into the grass and then a lug is used to connect the 4mm2 earth cable to the electrode, forming the supplementary bond, no mechanical protection or anything. Not to mention running the risk of hitting services such as gas and water pipes, etc.
I understand the resistance of an earth electrode must be under 200 ohms, this isn't checked most of the time and when it is I usually find that several earth electrodes have to be daisy chained together in order to reduce resistance under 200 ohms.
The CAI state that the resistance of the outer conductor of the coaxial cable to the MET must not exceed 4 ohms.
Is it just me or does anyone else see an issue here?
I've always had trouble getting my head around the need to earth bond TV systems, I understand that by running coaxial cables to each property in a block of flats you essentially create an electrical circuit that needs to be made safe buy typically the max voltage you are working with is 18V.