Can you guys tell me. Would you normaly removed light bulbs whilst do a insulation resistance test. Also what about fittings that use transformers??

Thanks.
 
You can test the board as a whole and cross out the bit on cert that has P-N P-E N-E and write under it P-N + E then on CU link P-N with link wire that way all bulbs trannys etc can be left in ! Sorted !
Also it is exeptable to drop test voltage to 250v for pelv/selv
Or you can remove all bulbs, plugged in equipment, fuses in fused spurs etc and do a 500v test as norm between P-N P-E N-E if no selv/pelv etc but its always good practice to do a 250v test first just in case youve left a bulb in, item plugged in, fuse left in fused spur etc.
 
Last edited by a moderator:
depending on the size of the insallation and number of transformers you could test l-n with the switches open and record a limitation on the cirt
as kung said try 250v first before you damage anything
 
As was mentioned somewhere else here before just remember that the 250V on your meter is probably 250V DC so some electronic equipment will not like it anyway so be careful.
 
just to add, ins res teting is probally the most awkward test to perform in my opinion always get poor readings because there is something you missed still in circuit...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
insulation resistance testing
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
stevo09,
Last reply from
kung,
Replies
7
Views
4,086

Advert

Back
Top