Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen appliances:

Hob
Oven (below 2kW)
Fridge/Freezer
Dishwasher
Washing machine
Extract Hood

For the hob, I intend to connect it to a cooker connection unit (located below the counter) and then to a 45A cooker unit (above the counter) on a dedicated circuit.

As for the remaining appliances, my plan is to wire them to unswitched 13A sockets (positioned below the counter) and then connect them to a 6-Gang grid switch, which will be part of a 32A ring circuit.

Now, I have concerns about the potential load being too high for a single circuit. Is it possible to establish two separate circuits for the grid switch without the need for an ugly warning notice?

Additionally, I've been pondering whether placing all these appliances on a 32A ring circuit might result in the 13A fuse in the appliance plug blowing first in case of an overcurrent issue. This would require users to remove the appliance and replace the fuse. Any thoughts on this matter?
 
Most appliances come with a melded on plug top which is recommended stays on as part of the warranty. I try not to cut any plug tops off unless I absolutely have to.
For a multi way grid you can take a couple 20amp radials to the grid to spread the load a bit. just make sure everything is labelled at the board and you can even put some stickers on the back of the grid
 
Most appliances come with a melded on plug top which is recommended stays on as part of the warranty. I try not to cut any plug tops off unless I absolutely have to.
For a multi way grid you can take a couple 20amp radials to the grid to spread the load a bit. just make sure everything is labelled at the board and you can even put some stickers on the back of the grid
I won't be cutting the plug tops, I will be plugging them to 13A unswitched sockets.

As for the gird switch, BS7671 section 537.1.2 states "Where an installation or an item of equipment or enclosure contains live parts connected to more than one supply, a durable warning notice shall be placed in such a position that any person, before gaining access to live parts, will be warned of the need to isolate those parts from the various supplies unless an interlocking arrangement is provided to isolate all the circuits concerned." This tells me that the warning notice needs to go next to the grid switch.
 
20A isolator above worktop above each socket - can then have get them engraved with appliance type.

Also saves the congestion of a grid switch.
 
Additionally, I've been pondering whether placing all these appliances on a 32A ring circuit might result in the 13A fuse in the appliance plug blowing first in case of an overcurrent issue. This would require users to remove the appliance and replace the fuse. Any thoughts on this matter?

What makes you believe appliance fuses would be affected in these circumstances?

Protective devices at db tripping due to overloaded circuit or cumulative earth leakage would be a greater consideration.

It's not a circuit I'd be happy installing, with the possibility of one appliance fault taking everything else out.
 
What makes you believe appliance fuses would be affected in these circumstances?

Protective devices at db tripping due to overloaded circuit or cumulative earth leakage would be a greater consideration.

It's not a circuit I'd be happy installing, with the possibility of one appliance fault taking everything else out.
If I am protecting several appliances that have plugs with 13A fuses and a 32A RCBO ring at the DB, wouldn't the 13A fuse blow first if there was an overload due to one of the appliances?

How would you circuit the above listed appliances?
 
You wouldn’t.

The sockets are below the counter. The switches are above. Individual switches rather than a bank of 4 on one plate.
So you are saying have 4 switches as per below picture (on the right)?

I think a grid switch looks better and takes much less space.
1699258883955.png
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Kitchen grid switch help
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
38
Unsolved
--

Advert

Thread statistics

Created
ibra123,
Last reply from
ibra123,
Replies
38
Views
5,962

Advert

Back
Top