Hi all i have a problem on a kitchen ring that has been reconnected by a different firm on a complete rewire. The building has been rewired apart from a kitchen that was joined onto existing wiring. Problem is, one I don't have a ring and two, I get power but then it goes off after an hour or so, I play with the cable at the cu and it comes back on, but then goes off??
 
If you can “play” with the cable at the cu, and it comes back on…. Sounds like a loose connection. Get whoever worked on that back to put it right.

Not wanting to scare you unnecessarily, but a loose electric cable can lead to overheating, and then a fire.
 
Why do you say you don't have a ring? If only one or two conductors aren't continuous end to end then there's a bad connection somewhere and ergo your problem.

Also, if it works when moving stuff in the CCU then there maybe a bad connection with the ends of the RFC into the MCB or the Buzzbar is not inserted into the MCB properly.

Next time it goes dead try voltage testing the output of the MCB

Note - There may be more than one issue! wouldn't be the first time...
 
Last edited:
From previous posts I assume Phil is the sparks trying to solve the problem.
I'd want to know why moving a cable changes anything as a top priority. To state the obvious I assume you've checked the CU connections themselves are sound. Finding the first point on that leg and checking connections and all permutations of continuity and IR with the cable in various positions would be high on my list. Could be a damaged section of cable or loose connection(s).

Did you measure the ring integrity at the CU or at a socket? Check any connection you've touched.
Does the entire ring go dead sometimes or just a section of it?
 
was the joiner and a nail gun!!😩
If I could uninvent anything on a building site, the nail gun would be it! Joints vary from hardly tacked together at all to something that would survive a nuclear blast. The nails bend in all directions when fired in. I've seen them bend through 180 degrees and come back out of the surface of the wood, if they encounter a knot.
With the Part M regulations for switch height, the noggin in a stud wall is often right in the way, and these things don't make it easy to modify it. All the studwork I've built has been held together with 5 x 80mm screws.
 
One thing that I have not seen mentioned. If you do discover a ring of such be careful that the ring hot wires trace back to the same MCB, I have come across many circuits where the hots feed back into different MCB making the circuit live even though you think the circuit has been isolated. A simple plug in circuit tester will tell you if this is the case, before you further explore. Could be a loose connection where a cable is acting like a bi metal strip, when it heats up (due to a possible arch) it moves away from its contact, as already mentioned this type of fault can cause cables to burn out, and fires. GET IT CHECKED BY A PRO (if not one yourself)
 
One thing that I have not seen mentioned. If you do discover a ring of such be careful that the ring hot wires trace back to the same MCB, I have come across many circuits where the hots feed back into different MCB making the circuit live even though you think the circuit has been isolated. A simple plug in circuit tester will tell you if this is the case, before you further explore. Could be a loose connection where a cable is acting like a bi metal strip, when it heats up (due to a possible arch) it moves away from its contact, as already mentioned this type of fault can cause cables to burn out, and fires. GET IT CHECKED BY A PRO (if not one yourself)
See post 11.
 
You need to hire electricians who can pinpoint and fix electrical issues, It’s good to know some proper ways to reduce the risk of electrical problems. I had no idea that some of these things could help keep you safe.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
United Kingdom

Thread Information

Title
Kitchen Ring Main Problem
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
PhilCumbria,
Last reply from
DPG,
Replies
15
Views
2,675

Advert

Back
Top