Hi guys, just after some advice. Went to a job today with the description that one rcd on a dual board has tripped and when closed trips instantly, the customer was watching TV at night and all of a sudden the lights and sockets went under normal running conditions. I arrived today and the rcd, the lights(whole house as it's a bungalow) and the sockets had tripped. I flicked the sockets and the light back on and the rcd tripped I left the lighting circuit off and now the sockets and the rcd are working. I Removed all the bulbs and the rcd still tripped. Normally I would assume a borrowed neutral but as this was working perfectly fine up until last night I'm a little stumped, could this be a possible transformer fault on the spotlights? I have been in the loft and the wiring actually looks pretty good.
Cheers for any advice
 
No tests at all yet Lee, as my tester is being calibrated, I'm back Friday morning, tester an all. Just thought I'd ask the question and get a point in the right direction.
 
I though rats as well but I did a good visual inspection and the cables and the routes seem to be clear and good, no smells either
 
If there are 12v down lights my money is on burnt cables and/or transformers!

what you describe is a classic sign of this


or DIYer putting nails, screws or holes through cables!
 
Yes in the bathroom there 12v down lights Murdock, I've never come across a transformer failing could this cause a live to earth fault? And is it a common fault?
Cheers for the reply
 
Yes in the bathroom there 12v down lights Murdock, I've never come across a transformer failing could this cause a live to earth fault? And is it a common fault?
Cheers for the reply

It would be unusual for a lighting transformer to cause a live to earth fault (and therefore RCD tripping) as they're not normally earthed.
 
Yes in the bathroom there 12v down lights Murdock, I've never come across a transformer failing could this cause a live to earth fault? And is it a common fault?
Cheers for the reply

Really??

Burnt light cables.jpg

This one, the cable was so damaged by the heat, the live was in contact with the earth!
 
It would be unusual for a lighting transformer to cause a live to earth fault (and therefore RCD tripping) as they're not normally earthed.


I thought they were centre tapped and the metal enclosure would be earthed.
Cheers for the advice I'm back on Friday so I'll reply back Friday with a picture
 
if the rcd holds with just the lighting mcb off, then it looks like a l-e fault on the lights. look for a picture hung above a switch for starters.
 