Well clearly the fault lays with the supply cable to the first point, disconnect the first point completely and IR the supply cables. I bet you will have a dead short there.
if nothing then IR after that point, you will find the issue.

something is telling me that your not a sparky as you have not even mentioned about your tester or test results, all its still tripping!

eitherway think about getting an electrician in before you kill yourself or a family member
read back mate tester and results clearly mentioned , well n truly qualified 17th edition but thanks for the advice
 
Keen to know what it turns out to be. You must post it when you get to the bottom of it.
 
Ok a IR of 0.2Mohms is not a fault in the first run unless a mouse had lunch early, its a long distance short or even a fault through a lamp.

whats the LE and NE readings at CU, 1st point, 2nd point, 3rd point, etc, etc, etc
 
Funny you should mention that , when it was just the McB tripping 2 times in a row at a squeaky floorboard when stood on it tripped straight away but after that nothing now it's rcd , which made me think its worked its way through the neutral cable now causing Imbalance on circuit and not a dead short ,

Did you lift the floorboard to investigate ?
 
Interesting thread
A lot of sound advice being given and plenty of fairly poor advice too.....
Its obviously not a dead short if its staying on for 4 hours.
Its Obviously not a L/N to earth fault because its the MCB tripping not the RCD (originally)
The first thought that sprang to my mind was a faulty transformer somewhere. I found this the other day when a client complained of an MCB tripping occasionally (it took me about 10 minutes)
Its hard to imagine its a damaged cable because I can't see how you could short L and N without shorting the cpc at the same time....unless of course that part of the cable has no cpc....
It'll be interesting to see the outcome
 
Sorry guys been M.i.a

been an on going job here customer only ever available now n then for around a hour ,
Found fault which was on the loop feed cable going between the 4th-5th switch , still haven't rewired it yet will be doing so next week , I'm thinking rodent or trapped along side heating pipe at boiler
 
trapped behind heating pipe. like it. blame wet-pants then. LOL.
 
or keep flicking the MCB on and on till it clears the short.
 