You'd be just as quick to of disconnected all lights(there can't be many if this is domestic we are talking here) on the circuit and from the DB and has been said even if it means testing from point to point you will find the fault it may be at a termination or cable damaged it's not rocket science, you may even have to replace a length of cable God forbid, but find it you must you'll get there in the ,just break the circuit down.
 
You'd be just as quick to of disconnected all lights(there can't be many if this is domestic we are talking here) on the circuit and from the DB and has been said even if it means testing from point to point you will find the fault it may be at a termination or cable damaged it's not rocket science, you may even have to replace a length of cable God forbid, but find it you must you'll get there in the ,just break the circuit down.

Had the same thing a while back, builder had put a screw through a cable when fixing a batten up for a new ceiling. Disconnected the whole circuit at the first rose, then added and IR tested as I went until the faulty leg of cable showed up. Fairly straightforward to find after that.
 
You suggest r1r2 every point , not done that yet , firstly it was McB only and would trip after minutes now rcd and it won't stay on atall

I always R1+R2 at every point when carrying out a CU change. Amazing how many times I've found breaks in the cpc which must have been there for years.
 
Whats with this test each bit individually malarky? Split the circuit in half find the faulty half, split the faulty half and find the faulty half of that etc etc until you isolate the fault.
 
I was assuming there would only be half a dozen lights or so, I agree your method is the best way forward but I was trying to give him a sure fire way of eliminating light by light as he seems a bit stumped and your (the best method) just might confuse him if the lights are dotted all over the show lol
Whats with this test each bit individually malarky? Split the circuit in half find the faulty half, split the faulty half and find the faulty half of that etc etc until you isolate the fault.
 
Sorry but I just refuse to cater for people who can't grasp basic concepts and don't have the ability to problem solve without a comfort blanket!
 
Yeah you're right, I should of stuck with the "get your tester out" as had already been said lol
 
Whats with this test each bit individually malarky? Split the circuit in half find the faulty half, split the faulty half and find the faulty half of that etc etc until you isolate the fault.

Half split technique is great, just so long as the circuit can be identified in that way.
I think the point that everyone is trying to make, is that "testing" of some kind is the way to go. Would still be interested to know what tests were carried out when the CU was installed...
 
if theres one thing i have learned about changing consumer units on houses after that job the other week , its to test absolutely everything before touching it , and then test everthing again after connections to new board before switching on , its not worth the grief to just batter on and do it and hope its ok ,thats how you end up on here in a panic , haha
 
racking my brains went back today testing at various points opening the feed cables at each switch one at a time , couldnt narrow it down to a certain cable or area , disconnected all switch wires(including n&e) still trips stays on for 3-4 hours today then trips ,

could be sitting with all switch wires out still trips :S
 
Well clearly the fault lays with the supply cable to the first point, disconnect the first point completely and IR the supply cables. I bet you will have a dead short there.
if nothing then IR after that point, you will find the issue.

something is telling me that your not a sparky as you have not even mentioned about your tester or test results, all its still tripping!

eitherway think about getting an electrician in before you kill yourself or a family member
 