Sorry guys been M.i.a

been an on going job here customer only ever available now n then for around a hour ,
Found fault which was on the loop feed cable going between the 4th-5th switch , still haven't rewired it yet will be doing so next week , I'm thinking rodent or trapped along side heating pipe at boiler

Had a similar fault and situation a few months ago, could only ever spend an hour or so at the property, never ideal. Also, was never really a fault when I was there, was getting a 70meg IR and nothing lower, once it was in use for a few hours though it was then tripping, and found a multitude of small faults with nicked insulation, loose earths, loose connections, even an earth being used as a neutral link!

Was a squashed cable on top of a central heating pipe in the end, would have been solved a lot quicker and cheaper for them if they'd have told me the truth when I asked if they'd ever had a flood. Was being squashed more and more every time anyone walked along the upstairs passageway.
 