polo1
Hi, anyone have any experince of these? I understand that a Type C breaker may be best? I've been asked to install a system of 5 x 50w on a 300va transformer witha run of approx 10m from the board to the transformer.
Any recommendations on make, size & type of breaker etc?
Regards
If you allow *6 times for inrush on a 300VA that’s 7.8A. A type B 6A should handle that with no problem. Inrush is the first few cycles.
I don't like these systems meself but if it's what the client wants then shove it in just like Tony said
Thanks Tony. Believe it or not, I've had an email from the client - they want 10 of these....yes, 10 x 5, 50w units! It's a museum and they are apparently to be used for exhibit lighting.
Is there likely to be a problem in having more than one unit on a suitably sized circuit? ( I don't yet know what the switching arrangements are to be).
Regards
Spilt as required then. Several MCB’s make sense.
Switch that lot in one go then a single MCB won’t cope.
As Tony said, split up the circuits as much as possible to avoid nuisance tripping on start up.
We did a job similar to this for the National Trust a couple of years ago and had the same problem, so ran in some extra feeds and switched each transformer seperately.