Hi, recently carried out an eicr at a rented property. There were 5x 1mm in a 6amp mcb for lighting.. my question is what code should I be looking at for this??
I am sure I have heard someone mention or read somewhere about overpopulating an mcb should be a code 2... but then i have also heard it’s all counted as 1x circuit so all the lights to the property are on 1x circuit.. which would be a code 3 recommendation they should be split.. advice would be welcomed.

cheers
 
If its fed from a single device it is one circuit. If in your professional opinion the conductors are adequately terminated and provided with fault and overload protection then no code is appropriate. There have been numerous debates here on the claims that 'multiple circuits' cannot be connected to a single device, ignoring the fact that it is multiple conductors forming one circuit, not multiple circuits. Nowhere do the regulations specifically prohibit this arrangement, nor do they require more than one lighting circuit in an installation.
 
A lighting circuit is a radial with several branches off whether from a switch or looped at the light. This one is just branched from the source.

why is it like this though? Is there shared neutrals where doubling up the circuits solved the problem, or is there another damaged 6A breaker that the circuit has been moved from as a “temporary” fix.
 
I’d say it’s 5 radial circuits and test at the extremity of each one....they will all be different lengths, different installation methods with branch’s etc giving different readings.....
 
I’d say it’s 5 radial circuits and test at the extremity of each one....they will all be different lengths, different installation methods with branch’s etc giving different readings.....
You test at the extremity of each branch and record the highest, just like you would with a lighting circuit that leaves the CU on one cable, and then splits multiple ways.
 
Yeh 5 final circuits in 1x 6amp mcb. Looks like they have just added to the installation over the years, but instead of upgrading board for more ways, they have just put them all in 1.
Common occurrence unfortunately.
 
Yeh 5 final circuits in 1x 6amp mcb. Looks like they have just added to the installation over the years, but instead of upgrading board for more ways, they have just put them all in 1.

There's absolutely no problem with that, as long as the circuit isn't overloaded. Used to be a maximum of 12 lamps for a 6A MCB, but this has become irrelevant with first cfl, and now LED lamps, although inrush still has to be considered.
I would make a comment, however, if this is the only lighting circuit.
 
Hi, recently carried out an eicr at a rented property. There were 5x 1mm in a 6amp mcb for lighting.. my question is what code should I be looking at for this??
I am sure I have heard someone mention or read somewhere about overpopulating an mcb should be a code 2... but then i have also heard it’s all counted as 1x circuit so all the lights to the property are on 1x circuit.. which would be a code 3 recommendation they should be split.. advice would be welcomed.

cheers
An MCB supplies a circuit, so anything connected to it is deemed a circuit regardless of how many wires there are, not an ideal situation, but seen it loads of times.
 
Last edited:
5 conductors physically into an mcb I can see... the corresponding neutrals into one hole of the neutral bar? Don’t think so.
So the neutrals won’t match the circuit number.

So if this one circuit was one cable from the CU to a nearby joint box, which then split 5 ways.... is it 1 or 5 circuits?
 

Reply to More than 1 circuit on mcb in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock