Discuss No cpc on lighting and no neutral continuity on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net
Do you know which sockets/outlets the break is between? as if you intend to change the protective device to 20A the NICEIC will take a dim view of the live being left as a ring you will need to test as two radials below earth loop limit. The loading, diversity and distribution of
the sockets would be a factor especially as it is feeding the kitchen.
As above, a faulty ring energised with a lower value ocpd is still an energised circuit with known faults.
The fault was already energised before being discovered, the addition of a 20a OCPD would in my opinion be an acceptable temporary measure as long as the inspector can see that a plan is in place to rectify.
I have noted on the EIC that these need rectifying. And the client is a family friend who will listen to my advice. I was also going to use this job to show NICEIC inspector for domestic installer, as is the only one close enough that fits the criteria Would you advise that I do these remedials before the inspection, will he out right tell me to do one or accredit me once I prove the remedials are done? Thanks
Yes, inspector will make you fix these issues and will lecture you, the installation has to be fit enough for the consumer board so fault trips meet regulation requirements. Also the regs have set in place that all lighting be earthed, I think it will be introduced in the 18th edition. Plus you have to notify building authority, so if anything does go wrong, your name is on the papers.
I believe the requirement for protective conductors in lighting circuits was introduced in 1966.
In your situation I would advise the customer that the installation has to be checked as the consumer board is different to the previous one. It has to meet a particular standard before it can be changed over, otherwise the board will not work as it should, then a new board just defeats the object even if it is metal.
Oh, I mean that if there was no CPC before it was advised that no metal fittings were fitted, but now they have to be earthed no matter what. Even if there is no earth point, all cables in and out should be earthed with connector. For R1 +R2 reasons cables in zones and walls be RCD protected.
Disagree 100%
Replacing a fuseboard, for one with RCD's will make the installation safer.........
The requirement for a cpc at every point is a current requirement.
The guidance to swap out to class 2 fittings on a circuit with no cpc is not in the regs.
Earthed with a connector?
New posts
Reply to No cpc on lighting and no neutral continuity on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Just to be clear… I am going to do the correct thing here and pay for the correct parts…. I just wanted to start the discussion. My particular...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...