And unless you take a bit of a scientific approach with additional testing it'll always be the very last socket that you open up with the dodgy connection. :)
 
  • Funny
Reactions: DPG
Decide which one you are going to start with, then change your mind and go for one at the other end. Then you will always find it at the first one. Simple. Not in the On-site Guide that one.
 
or a wood butcher hanging a cabinet above a socket. seen that t'other week. rawlplug and screw straight through a T/E 2.5mm.
 
  • Like
Reactions: DPG
I’ve checked all the Spurs/Sockets Murdoch. I’ll definitely have to make it two radials as I’m certain it’ll be in a buried joint box.
 
Agreed, but was looking for something obvious, disconnection at a spur/Socket. Will split the ring and work my way back to the board. Cheers
 
  • Like
Reactions: DPG
Do you know which sockets/outlets the break is between? as if you intend to change the protective device to 20A the NICEIC will take a dim view of the live being left as a ring you will need to test as two radials below earth loop limit. The loading, diversity and distribution of
the sockets would be a factor especially as it is feeding the kitchen.

As above, a faulty ring energised with a lower value ocpd is still an energised circuit with known faults.
The fault was already energised before being discovered, the addition of a 20a OCPD would in my opinion be an acceptable temporary measure as long as the inspector can see that a plan is in place to rectify.
 
I have noted on the EIC that these need rectifying. And the client is a family friend who will listen to my advice. I was also going to use this job to show NICEIC inspector for domestic installer, as is the only one close enough that fits the criteria Would you advise that I do these remedials before the inspection, will he out right tell me to do one or accredit me once I prove the remedials are done? Thanks
Yes, inspector will make you fix these issues and will lecture you, the installation has to be fit enough for the consumer board so fault trips meet regulation requirements. Also the regs have set in place that all lighting be earthed, I think it will be introduced in the 18th edition. Plus you have to notify building authority, so if anything does go wrong, your name is on the papers.
 
Yes, inspector will make you fix these issues and will lecture you, the installation has to be fit enough for the consumer board so fault trips meet regulation requirements. Also the regs have set in place that all lighting be earthed, I think it will be introduced in the 18th edition. Plus you have to notify building authority, so if anything does go wrong, your name is on the papers.

I believe the requirement for protective conductors in lighting circuits was introduced in 1966.
 
In your situation I would advise the customer that the installation has to be checked as the consumer board is different to the previous one. It has to meet a particular standard before it can be changed over, otherwise the board will not work as it should, then a new board just defeats the object even if it is metal.
 
I believe the requirement for protective conductors in lighting circuits was introduced in 1966.
Oh, I mean that if there was no CPC before it was advised that no metal fittings were fitted, but now they have to be earthed no matter what. Even if there is no earth point, all cables in and out should be earthed with connector. For R1 +R2 reasons cables in zones and walls be RCD protected.
 
In your situation I would advise the customer that the installation has to be checked as the consumer board is different to the previous one. It has to meet a particular standard before it can be changed over, otherwise the board will not work as it should, then a new board just defeats the object even if it is metal.

Disagree 100%

Replacing a fuseboard, for one with RCD's will make the installation safer.........
 
Oh, I mean that if there was no CPC before it was advised that no metal fittings were fitted, but now they have to be earthed no matter what. Even if there is no earth point, all cables in and out should be earthed with connector. For R1 +R2 reasons cables in zones and walls be RCD protected.

The requirement for a cpc at every point is a current requirement.
The guidance to swap out to class 2 fittings on a circuit with no cpc is not in the regs.
 
Oh, I mean that if there was no CPC before it was advised that no metal fittings were fitted, but now they have to be earthed no matter what. Even if there is no earth point, all cables in and out should be earthed with connector. For R1 +R2 reasons cables in zones and walls be RCD protected.
Earthed with a connector?
 
Oh, I mean that if there was no CPC before it was advised that no metal fittings were fitted, but now they have to be earthed no matter what. Even if there is no earth point, all cables in and out should be earthed with connector. For R1 +R2 reasons cables in zones and walls be RCD protected.
Earthed with a connector?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
No cpc on lighting and no neutral continuity on kitchen ring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
177

Advert

Thread statistics

Created
Muzza115,
Last reply from
Toneyz,
Replies
177
Views
17,767

Advert