Disagree 200% It's about his inspection not meeting the requirements for a board change.

So you are saying that you would tell a customer they can't have a new fuseboard because the lighting circuit doesn't have a CPC

Even if he had inspected it thoroughly before he could still have gone ahead and changed the CU
 
Yes, inspector will make you fix these issues and will lecture you, the installation has to be fit enough for the consumer board so fault trips meet regulation requirements. Also the regs have set in place that all lighting be earthed, I think it will be introduced in the 18th edition. Plus you have to notify building authority, so if anything does go wrong, your name is on the papers.
Deleted
 
I believe the requirement for protective conductors in lighting circuits was introduced in 1966.
What he said^^^^^^^^^^^^^^^^
 
  • Like
Reactions: DPG
Before, on a certificate, no CPC to lighting was classed as a c3 with advice of no metal light fittings. But in the 18th it will be a c1 or c2. Basically a fail

Really ?????????????????????????????????
 
I would not change it untill rectifications are made first.

So poor Mrs Jones, who can't deal with BS 3036 fuses anymore will HAVE to have her lighting rewired before you would change a fuseboard ...........................

Bad practice IMHO

What do your scheme say?
 
Disagree 100%

Replacing a fuseboard, for one with RCD's will make the installation safer.........
What he said^^^^^^^^^^^^^^^^^^^^^^^^^^^
 
Really ?????????????????????????????????
Yes I've seen it on old certs, even that made me confused. But I made inquiries, the inspector was right. However all has to be earthed. In a domestic all circuits are RCD protected but if there is a break in the R1 + R2 it defeats the objects
 
Yes I've seen it on old certs, even that made me confused. But I made inquiries, the inspector was right. However all has to be earthed. In a domestic all circuits are RCD protected but if there is a break in the R1 + R2 it defeats the objects

Seen what exactly on old certs?
 
So poor Mrs Jones, who can't deal with BS 3036 fuses anymore will HAVE to have her lighting rewired before you would change a fuseboard ...........................

Bad practice IMHO

What do your scheme say?
The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.
 
So poor Mrs Jones, who can't deal with BS 3036 fuses anymore will HAVE to have her lighting rewired before you would change a fuseboard ...........................

Bad practice IMHO

What do your scheme say?
The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.
 
So poor Mrs Jones, who can't deal with BS 3036 fuses anymore will HAVE to have her lighting rewired before you would change a fuseboard ...........................

Bad practice IMHO

What do your scheme say?
The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.
 
The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.

I've seen a RCD protecting a lighting circuit (with no cpc) trip a RCD....

Do you understand how RCD's work?
 
Before, on a certificate, no CPC to lighting was classed as a c3 with advice of no metal light fittings. But in the 18th it will be a c1 or c2. Basically a fail

This is irrelevant to this thread - the OP's doing a CU change , not an EICR
 
What do you base that statement on?
Regs, looking at old certs dated 2013 and then phoning up and asking the person issuing the certs that he passed an periodic inspection even though there is no earth to lighting. I always believed with my old company that you had to earth no matter what. Apparently you could get away without CPC to lighting before, as long as there are no metal switches or fittings. That's all changing now.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
No cpc on lighting and no neutral continuity on kitchen ring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
177

Advert

Thread statistics

Created
Muzza115,
Last reply from
Toneyz,
Replies
177
Views
17,767

Advert