hey guys, I had a quick search but couldn’t find any posts about this.
I recently done an inspection on a domestic property and found the electrical meter was outside in a service cabinet and the fuseboard was inside more than 5m away. I recommended installed a fused disconnector at the meter to comply with regulations and also for convenience if the fuseboard had to be isolated.
I would say this should be non combustible but I still see a lot of the plastic styles of these switches available. Such as LEMSF100.
Is it possible for this to be installed as it is outside the home? I think I would rather install a metal one anyway but curious to hear your opinion on the matter
 
We've debated this subject before; some suggest a switch fuse is not similar switchgear assembly, some suggest a meter box (plastic)flushed into an outside wall is not within a domestic premise.

When I was in a scheme, I did seek guidance from their technical, and the response was that the designer would have to make that assessment, as whether 421.1.201 applied in these circumstances.

So you can ask the question, and would probably get a lot of responses that it doesn't, but its for you to decide.
 
We've debated this subject before; some suggest a switch fuse is not similar switchgear assembly, some suggest a meter box (plastic)flushed into an outside wall is not within a domestic premise.

When I was in a scheme, I did seek guidance from their technical, and the response was that the designer would have to make that assessment, as whether 421.1.201 applied in these circumstances.

So you can ask the question, and would probably get a lot of responses that it doesn't, but its for you to decide.
So in a nut shell the Scheme couldn't / didn't offer advice because they didn't know the answer, left the decision up to the installer, Buck passing of the highest order, and you pay hard earned dosh to belong to a Scheme, yes it's old, I agree, but true non the less.
 
So in a nut shell the Scheme couldn't / didn't offer advice because they didn't know the answer, left the decision up to the installer, Buck passing of the highest order, and you pay hard earned dosh to belong to a Scheme, yes it's old, I agree, but true non the less.

Well, its kinda of a bit vague, 421.1.201. If the grown ups at the IET etc, want to make things clear as mud, perhaps you should lay the blame at their door.
 
You shouldn't fit any metal in a meter cabinet as earthed metalwork increases the hazards for DNO operatives who work live in the cabinets.
 
But the meter cabinet isn't the DNO's property, it belongs to the consumer.
Can’t speak for them all Dave but working on some new builds in Sheffield around 3 years ago, we had to get the builder to install a separate meter cabinet to house the switch fuse isolator as the DNO refused to allow it in along side their metering equipment.
Or rather the metering company refused as it’s their equipment so we complied with their wishes
 
Can’t speak for them all Dave but working on some new builds in Sheffield around 3 years ago, we had to get the builder to install a separate meter cabinet to house the switch fuse isolator as the DNO refused to allow it in along side their metering equipment.
Or rather the metering company refused as it’s their equipment so we complied with their wishes

Interesting, and I'm sure you could have argued the point if you wanted to but would probably turn out to be more hassle than it's worth.

The simple way to look at it is that the consumer has buy the meter box outright therfore it belongs to them.
 
Interesting, and I'm sure you could have argued the point if you wanted to but would probably turn out to be more hassle than it's worth.

The simple way to look at it is that the consumer has buy the meter box outright therfore it belongs to them.
Totally agree.
However arguing the case with the builder after the metering company has told them we can’t utilise the cabinet was futile.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

WallaceP

Arms
-
Joined
Location
Here
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Non combustible switchgear
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21
Unsolved
--

Advert

Thread statistics

Created
WallaceP,
Last reply from
Midwest,
Replies
21
Views
3,341

Advert

Back
Top