Well time has come to further my knowledge, now I know I was taught these at college but once i left i realised it was all about thinking from the neck down! So I know the rule of thumb is .8 but how do I apply these into calculations:freak:
 
That would be an approximation of ZS.

R1+R2 is a measurement of resistance not impedance.

To be fair I was being a little cheeky, no offence meant. Just a gentle poke in the ribs ;-)
 
no offence taken!


the reason for the question is I done most of my 2391-20 this year i was all good till the power factor gets thrown in it throws me been searching google for days to no avail
 
I must admit, the reason I went to this thread is that although I can get all the power factor questions easily; the issue for me is I have no idea how to apply them to real life!!!!

I was hoping someone else would explain in this thread =-)
 
Power factor is the value given to a capacitive or inductive load.
Power factor of a resistive load is 1.
Putting it simply it is a number that represents the power output of a load to the power being taken from the supply.
 
Can I tag a small question on to this?

I have a device with two lights next to each other providing heat to a plate (GU10 50w).

As our mains supply is a bit ****, I was thinking of putting a cap in series with the second light pushing the dips in voltage slightly out of phase with the first lamp.
Am hoping this would average out the flicker a bit as both lights will flicker at different times.

This is another power factor question, but any idea what calc I should be doing to get the cap size?

I do not want to push the pf too far out or the light will start to dim (I think), but in turn want a time delay.

So anyone care to help?
 
A halogen lamp is incandescent, PF plays no part in it.
 
Last edited by a moderator:
Can I tag a small question on to this?

I have a device with two lights next to each other providing heat to a plate (GU10 50w).

As our mains supply is a bit ****, I was thinking of putting a cap in series with the second light pushing the dips in voltage slightly out of phase with the first lamp.
Am hoping this would average out the flicker a bit as both lights will flicker at different times.

This is another power factor question, but any idea what calc I should be doing to get the cap size?

I do not want to push the pf too far out or the light will start to dim (I think), but in turn want a time delay.

So anyone care to help?


Wot Tony said...Tungsten lamps are a resistive load,you could only produce a lead/lag effect with discharge lighting....ie fluorescent lamps control gear.
 
Power factor applies to inductive loads, where coils are used to provide a large back emf to fire up discharge tubes and then used to limit the current flow across the tubes. Motors being inductive also require pf correction.

Since a capacitor provides a leading power factor, it counteracts the laging pf of the coil, to a degree. You don't want a perfect correction since this can create large oscillating currents and voltages across the components, usually an acceptable value would be around 0.93.

Most individual components with coils and capacitors as a rule of thumb provide a basic pf correction of 0.85. This in most cases is suitable for small installations but would require further correction, at the main incomer for large installations
 
Power factor applies to inductive loads, where coils are used to provide a large back emf to fire up discharge tubes and then used to limit the current flow across the tubes. Motors being inductive also require pf correction.

Since a capacitor provides a leading power factor, it counteracts the laging pf of the coil, to a degree. You don't want a perfect correction since this can create large oscillating currents and voltages across the components, usually an acceptable value would be around 0.93.

Most individual components with coils and capacitors as a rule of thumb provide a basic pf correction of 0.85. This in most cases is suitable for small installations but would require further correction, at the main incomer for large installations


so how do you put this 0.85 into a cable calc?
 
so how do you put this 0.85 into a cable calc?

For motors the info is on the nameplate kW=XX and Pf=XX, or kVA=XX and pf=XX or kVA=XX and kW=XX
A simple couple of equations are used:

1/ kVA= kW/pf
2/ I = kVA/V

For lighting the power is usually quoted in Watts so apply the above formula without the 'k'

The important thing is the current in the cable which is the apparent power, not the power consumed by the load.
 
I am not trying to correct the power factor of a halogen, I am trying to ruin it.

Adding a cap will put a slight delay in the system. This delay will put the flickers out of phase with each other, 'hopefully' reducing the visibility of it.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
power factor correction
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
26

Advert

Thread statistics

Created
The Ranger,
Last reply from
nil26,
Replies
26
Views
6,946

Advert

Back
Top