I have just had a call from a company who are looking at installing some elctric gates at the bottom of a long drive.
They have asked me to price for 100m armoured cable (its a looooooong drive).

I asked the guy what amps i need to power the gates and he replyed 6a.(prolly less than this but thats what he said)
They want the cable clipped to the fence down the side of the drive.

I was just looking at what the voltage drop may be for this cable so turned to page 338 and 339 of the bgb.

Now i like to use 3 core armoured cable i was wondering which colomn i should use
p339 colomn 2 says 2 core dc, colomn 3 says 2 core single phase ac and colomn 4 says 3 or 4 core 3phase,
no colomn for 3 core single phase.

do i use cololmn 3 or 4?

Thanks in advance guys
 
treat it as 2 core a.c. single phase. the 3rd core is used as cpc, so will not count in the VD equation. top of my head, at 6A yo'll get 12V drop using 2.5mm
 
I would go with 4mm TBH. No doubt they may want automatic lighting connecting etc and as mentioned possibly a socket as it's always handy to have.

How are they controlling the gates?
 
I would go with 4mm TBH. No doubt they may want automatic lighting connecting etc and as mentioned possibly a socket as it's always handy to have.

How are they controlling the gates?

as strima says,you may want some multicore control cables down there.long way to walk to open the gate for visitors..
 
The last set of gates I looked at were controlled by remote fobs and door entry type system wired (camera and all the gubbins) in Cat5, only a 25m run so not sure how Cat5 would hold up over 100m.
 
The last set of gates I looked at were controlled by remote fobs and door entry type system wired (camera and all the gubbins) in Cat5, only a 25m run so not sure how Cat5 would hold up over 100m.[/QUOT


wouldn't like to bury cat5 direct in the ground.LOL>
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Power To Electric Gate
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19
Unsolved
--

Advert

Thread statistics

Created
ample current,
Last reply from
ample current,
Replies
19
Views
11,045

Advert

Back
Top