davino
can somone tell me how to mesure pfc for a domestic property need this asap!!!!!
thanks in advance
thanks in advance
Disconect Main Earth. Put meter across Earth incoming (met) Connect other leads to Phase conductors do test. Then connect Earth and Neutral test leads together and connect to neutral phase conductor, connect the other lead to Line Phase conductor.
Test again. Wich ever is the highest reading in Ka record that on the test results.
Don't forget to re connect the main Met.
All these tests done with power on cons unit OFF
You could also buy Guidance Notes 3 it will help you with all aspects of Testing & Inspecting
take a Ze reading.
230v divided by your Ze reading. then divide this answer by 1000.
Thats your fault current.
Ohms law.
Disconect Main Earth. Put meter across Earth incoming (met) Connect other leads to Phase conductors do test. Then connect Earth and Neutral test leads together and connect to neutral phase conductor, connect the other lead to Line Phase conductor.
Test again. Wich ever is the highest reading in Ka record that on the test results.
Don't forget to re connect the main Met.
All these tests done with power on cons unit OFF
I dont understand. surely V=IROhms law applies to DC supply & not AC
although the ballpark figure won't be far off, it still isn't entirely accurate
saying V=I.R is fine, for DC theory
it is 100% correct, but i assure this is the formula for DC. when considering AC it becomes complex when you have to consider much more, ie. impedance, frequency, reactance, inductance etc.
Uksel - Just as the Nominal Voltage is oscillating then so is the Current - that's why its called "Alternating Current" as it flows in opposite directions each half cycle. It is therefore just as valid to describe the nominal voltage of the UK supply as 230V RMS as it is to refer to an alternating current of 100A RMS.
When using Ohms law to calculate an AC current flowing in a load as a result of an AC Voltage we replace "Resistance" by "Impedance". Impedance is a complex resistance which is related to how the load responds to an alternating current. The load's capacitance and inductance as well as resistance all contribute to its impedance. As capacitive and inductive reactance are related to the frequency of the alternating current/voltage then there can be a frequency dependence on the equation.
For PFC we assume that at 50Hz the impedance of the source (ie Ze) is a simple resistive value.
So Ipfc=Uo/Ze
Disconect Main Earth. Put meter across Earth incoming (met) Connect other leads to Phase conductors do test. Then connect Earth and Neutral test leads together and connect to neutral phase conductor, connect the other lead to Line Phase conductor.
Test again. Wich ever is the highest reading in Ka record that on the test results.
Don't forget to re connect the main Met.
All these tests done with power on cons unit OFF
can somone tell me how to mesure pfc for a domestic property need this asap!!!!!
thanks in advance
can somone tell me how to mesure pfc for a domestic property need this asap!!!!!
thanks in advance
you dont disconnect earthing conductor for pfcam guessing parallel paths???
I have my niceic inspection tomorrow and would like to know how to calculate your cable length from the results you have measured on the cert? Can you help